  1. #1
    adam5365's Avatar
    adam5365 Guest

    Hot gas defrost



    Last year a local farmer bought lorry fridge body to store turkeys leading up to christmas.
    some one came to "make it work" but butchered all electricals fitting a small control unit with control lines for compressor,evaporator coil fans and defrost.

    1)The compressor contactor was wired directly from this external control bypassing the pressure switch and motor overload,I am currently rewiring reverting back to the 12v control system run from the new controller.
    is it a good idea to re connect the pressure switch?

    2) The hot gas system is all still "plumbed in" but not wired up as it has been butchered by another party, so
    i have no idea how to rewire it.
    are there any particular things regarding solanoid valve timing which one first, delay after change before compressor restarts?

    Any help would be greatfully recieved

    Sorry didnt realise i could edit post added more details in a new post (no 6)in this thread OOPS!!!
    Adam



    added 03/03/06

    How very rude of me, I am most grateful for your help
    especially djbe,referjohn and themo690.
    djbe because he fully read and understood my post in that all circuit boards were smashed and so providing me with a full description of what connections i needed to make where, to get the unit up without the damaged control circuits.
    referjohn and thermo690 because they took the time to find and send me the original wiring diagrams.
    The unit worked for three days over Christmas without any probs although the defrost system is not yet sorted out.
    During the summer wedding season the fridge will run almost continually so I will have to get around to setting up the defrost.
    Please accept my apologies for my ignorance
    Adam
    Last edited by adam5365; 03-03-2006 at 08:44 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hot gas defrost

    Connecting in the pressure and overload switches would be a GOOD idea as they will help protect the compressor from damage.

    I'm not sure about the defrost solenoid valves as would need to see them or a sketch or photo to understand the layout.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Hot gas defrost

    Hi Adam5365,

    I am assuming that it is the original reefer unit on the body and not something someone's added on after the body was taken off.

    If so, give us the details of the unit and i am sure one of us will have a wiring diagram for it

    Regards

    Fatboy

  4. #4
    adam5365's Avatar
    adam5365 Guest

    Re: Hot gas defrost

    Thanks guys
    Im back at the farm today will take some pics and do a sketch

  5. #5
    Join Date
    Oct 2005
    Location
    kent , england
    Posts
    27
    Rep Power
    0

    Re: Hot gas defrost

    if you put in an elliwell cotroller with a hot gas defrost control facillity on it you should be able to wire everything back to the controller and barring a few minor adjustments to the paremeters, everything should be set up automatically to run properly.
    chill out it's only a fridge

  6. #6
    adam5365's Avatar
    adam5365 Guest

    Re: Hot gas defrost

    Guys
    scuse me if I dont use the correct name for stuff and things but heres some info on the system

    The unit is original, it is a Carrier Frigking zephyr 300. the pipes that lead to the engine compressor have been blanked off (3)in pic dc004,

    what is, and how do i connect the ?at(1)in pic dc004,

    I assume that (1)is the hot gas solanoid

    pipe(4) is from the mains compressor

    The fridge doc attatched is how the wiring stands at the moment, apart from a switch on the door to kill the evaporator fans and turn the inside light on that I fitted today.

    the doc also contains layout of the pipes, not brill but I hope you understand it.
    (1) compressor
    (2)orange thing ((2)in dc004)
    (3)hot gas solanoid ((1)in dc004)
    (4)condensor
    (5)evaporator

    not shown on this layout( i forgot it )is a pressure switch tee'd into the pipe from ((2)in dc004) the orange thing to the condensor.

    inside one of the electric bays there is a diag of relays on the cicuit board that was smashed, part of the diag shows a relay wired to reverse the mains three phase compressor ,why would this need to be done and do i need to set this circuit back up?

    the controller that was fitted (badly)last year is an eliwell ID 974 data sheet at
    http://www.invensyscontrolseurope.co...%206-03%20.pdf
    Thanks again for you time
    Adam
    Attached Images Attached Images
    Attached Files Attached Files
    Last edited by adam5365; 21-12-2005 at 09:34 AM. Reason: more details remembered

  7. #7
    Join Date
    Oct 2005
    Location
    united kingdom
    Posts
    48
    Rep Power
    0

    Re: Hot gas defrost

    Quote Originally Posted by adam5365
    Last year a local farmer bought lorry fridge body to store turkeys leading up to christmas.
    some one came to "make it work" but butchered all electricals fitting a small control unit with control lines for compressor,evaporator coil fans and defrost.

    1)The compressor contactor was wired directly from this external control bypassing the pressure switch and motor overload,I am currently rewiring reverting back to the 12v control system run from the new controller.
    is it a good idea to re connect the pressure switch?

    2) The hot gas system is all still "plumbed in" but not wired up as it has been butchered by another party, so
    i have no idea how to rewire it.
    are there any particular things regarding solanoid valve timing which one first, delay after change before compressor restarts?

    Any help would be greatfully recieved
    hi adam
    all you need is a little controller an elliwell or similar.
    you can then wire in your saftey switches to the controller and if you get one with defrost you can use your bypass valve, wire the controller as the switch live or ground to the pull in coils of the contactors for compressor/fans/defrost fit your sensors, set your parameters job done
    Shushhhhh!!! it seems to be working now

  8. #8
    Join Date
    Oct 2005
    Location
    united kingdom
    Posts
    48
    Rep Power
    0

    Re: Hot gas defrost

    Quote Originally Posted by evaporator
    hi adam
    all you need is a little controller an elliwell or similar.
    you can then wire in your saftey switches to the controller and if you get one with defrost you can use your bypass valve, wire the controller as the switch live or ground to the pull in coils of the contactors for compressor/fans/defrost fit your sensors, set your parameters job done
    sorry shane wrote reply before i see your post
    Shushhhhh!!! it seems to be working now

  9. #9
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: Hot gas defrost

    Shane,

    I think i've got some Zephyr 300 details kicking around somewhere. I'll check tommorow and let you know.

  10. #10
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Hot gas defrost

    the id 974 should be ok for your purposes , i would forget all the previous wireing others have done , pull it out and start again , make sure you run the compressor through the contactor still and use the controll signal from the elliwell to controll the contactor as the contacts on the elliwell will probably not cope with the compressor amps and fail a lot quicker. the fans and defrost solenoid should be ok straight through the controller though.

    hope this helps

  11. #11
    Join Date
    Oct 2005
    Location
    united kingdom
    Posts
    48
    Rep Power
    0

    Re: Hot gas defrost

    Quote Originally Posted by djbe

    Zephyr 300 details kicking around somewhere. .
    Hi Djbe
    that was very well spotted from that photo, i have not seen one for over ten years
    Shushhhhh!!! it seems to be working now

  12. #12
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: Hot gas defrost

    Sorry Adam,

    I don't have a any Zephyr 300 details. The closest I have is Zephyr 200 but, to be honest these are photocopies of photocopies and unless you are clued up on Carrier equipment even originals are clear as mud

    The only thing I can suggest is the same as Shane & Evaporator. Keep your ID974 controller and try the following:

    1. Wire the disconnected safety pressure switch (the orange thing) in series with the compressor contactor switching feed.

    2. Wire the hotgas solenoid coil to the defrost output of the controller. This solenoid should be 12 or 24v (I assume you still have the mains transformer in the system). Set the ID974 up for hotgas defrost. You will still need the probe in the evap. for termination.

    3. If the evaporator fan relay is already switched by the ID974 this should stop when it the unit goes onto defrost (you may have to check and adjust the parameters if this does not happen).

    4. Don't be afraid to rip all of the existing relays etc. out and start again if you have to, bear in mind that now the road operation of the unit has been removed it is very similar to a commercial refrigeration unit. The only real difference is the hotgas defrost and that the fans/control circuit will be 12/24dc.

    regards,
    djbe

  13. #13
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: Hot gas defrost

    Quote Originally Posted by evaporator
    Hi Djbe
    that was very well spotted from that photo, i have not seen one for over ten years
    Hi Evaporator,

    I'm not that clever mate. I only know it's a Z300 because Adam mentioned in a previous post

  14. #14
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: Hot gas defrost

    Can you confirm its a 400v 3 phase 12 or 24v system...if so email me off list.

    John.

  15. #15
    Join Date
    Mar 2005
    Location
    Austraia
    Posts
    48
    Rep Power
    0

    Re: Hot gas defrost

    Quote Originally Posted by adam5365
    Last year a local farmer bought lorry fridge body to store turkeys leading up to christmas.
    some one came to "make it work" but butchered all electricals fitting a small control unit with control lines for compressor,evaporator coil fans and defrost.

    1)The compressor contactor was wired directly from this external control bypassing the pressure switch and motor overload,I am currently rewiring reverting back to the 12v control system run from the new controller.
    is it a good idea to re connect the pressure switch?

    2) The hot gas system is all still "plumbed in" but not wired up as it has been butchered by another party, so
    i have no idea how to rewire it.
    are there any particular things regarding solanoid valve timing which one first, delay after change before compressor restarts?

    Any help would be greatfully recieved

    Sorry didnt realise i could edit post added more details in a new post (no 6)in this thread OOPS!!!
    Adam

    Hi please find attached the wiring diagram for this unit hope it helps

    Martin
    Attached Files Attached Files
    Last edited by thermo690; 14-01-2006 at 09:31 PM.

  16. #16
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: Hot gas defrost

    Hey Adam...

    Thanks for our help....glad you apreciated it

  17. #17
    Join Date
    Jan 2006
    Location
    UK
    Posts
    54
    Rep Power
    19

    Re: Hot gas defrost

    LoL ... perhaps he is stuck in reefer ....

  18. #18
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: Hot gas defrost



    ramble:ramble:ramble

  19. #19
    adam5365's Avatar
    adam5365 Guest

    Unhappy Re: Hot gas defrost


    How very rude of me, I am most grateful for your help
    especially djbe,referjohn and themo690.
    djbe because he fully read and understood my post in that all circuit boards were smashed and so providing me with a full description of what connections i needed to make where, to get the unit up without the damaged control circuits.
    referjohn and thermo690 because they took the time to find and send me the original wiring diagrams.
    The unit worked for three days over Christmas without any probs although the defrost system is not yet sorted out.
    During the summer wedding season the fridge will run almost continually so I will have to get around to setting up the defrost.
    Please accept my apologies for my ignorance
    Adam

  20. #20
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: Hot gas defrost

    Hey, Adam.
    No Problem, glad to see you got the problem solved and customer happy.

    John.

  21. #21
    Join Date
    Nov 2007
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Hot gas defrost

    Hello every one I'm having problems in supermarket with electric defrost the heater coils burn-out every 3 Mont's. so I want to convert the system to hot gas defrost
    So if any one can help me out Please let me know

Similar Threads

  1. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  2. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM
  3. Electric Defrost
    By iceman007 in forum Trouble Shooting
    Replies: 19
    Last Post: 12-06-2004, 09:34 AM
  4. Hot gas defrost
    By Volnei in forum Fundamentals
    Replies: 2
    Last Post: 18-05-2002, 12:26 PM
  5. Hot gas/Cool gas defrost
    By JONAH in forum Technical Discussions
    Replies: 9
    Last Post: 10-04-2002, 12:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •