    Maybe someone can assist with Vi ratio on Frck XJS120.

    Single stage economized NH3 compressor

    -30 C suction
    +35 C condensing

    What would be Vi solenoids be? all de-energized for 5.0 Vi?

    Thanks



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Frick XJS120 Vi ratio

    Hi Ranger,

    The two YY3 and YY4 solenoid valves of the Vi system shall be turned off as you mentioned.

    This is part of the screw compressor manual of the SABROE SAB120 which is Frick XJS120 block.


    "7.1.14. Volumizer II Vi control
    The compressor is equipped with a special internal control that automatically adjusts the compressor
    volume ratio to the most efficient of three available steps, (2.2, 3.5, or 5.0 volume
    ratio). This gives the compressor the ability to operate at varying operating conditions while
    minimizing power consumption by avoiding over or undercompression.
    Solenoid valves 3 and 4 control the Volumizer® II volume ratio control. Oil is internally ported
    to apply hydraulic pressure to two stepping pistons in order to move the moveable slide stop to
    the optimum position. The following chart shows the logic of solenoid operation to adjust the
    volume ratio.
    Vi YY3 YY4
    2.2 Energized Energized
    3.5 Deenergized Energized
    5.0 Deenergized Deenergized
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Frick XJS120 Vi ratio

    Quote Originally Posted by Sandro Baptista View Post
    Hi Ranger,

    The two YY3 and YY4 solenoid valves of the Vi system shall be turned off as you mentioned.

    This is part of the screw compressor manual of the SABROE SAB120 which is Frick XJS120 block.


    "7.1.14. Volumizer II Vi control
    The compressor is equipped with a special internal control that automatically adjusts the compressor
    volume ratio to the most efficient of three available steps, (2.2, 3.5, or 5.0 volume
    ratio). This gives the compressor the ability to operate at varying operating conditions while
    minimizing power consumption by avoiding over or undercompression.
    Solenoid valves 3 and 4 control the Volumizer® II volume ratio control. Oil is internally ported
    to apply hydraulic pressure to two stepping pistons in order to move the moveable slide stop to
    the optimum position. The following chart shows the logic of solenoid operation to adjust the
    volume ratio.
    Vi YY3 YY4
    2.2 Energized Energized
    3.5 Deenergized Energized
    5.0 Deenergized Deenergized

    Thanks Sandro,

    Its interesting as someone has them permanently energized on this one, so must be pretty inneficient
    at the moment!
    It was installed by York!!

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Frick XJS120 Vi ratio

    Maybe the electrical connections to the Quantum were not well done...or maybe the technician wanted fix the Vi and thought the regimen were about 0ºC/+35ºC...

    Maybe...maybe...maybe...
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Dec 2008
    Location
    chapeco
    Age
    39
    Posts
    62
    Rep Power
    16

    Re: Frick XJS120 Vi ratio

    hello, what e-mail for sending the manual, hugs

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Frick XJS120 Vi ratio

    Quote Originally Posted by diego palma View Post
    hello, what e-mail for sending the manual, hugs
    Thanks Diego, I have enough information for this model.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •