10-07-2012, 10:39 PM #1
Rhoss CHiller problem
Dear All
I have a problem with Rhoss chiller model : CWA / E 185
unit do not start and stopped at AL02
I do not have any manual , alarm list
please advice any manual will be usefull at : waseemnaamo@yahoo.com
Regards
-
10-07-2012, 10:57 PM #2
Re: Rhoss CHiller problem
sorry no manual- check continuity of thr flow switch, then safety circuits pump contacts- hp,lp switch- displayed water temp compare with actual temp
-
11-07-2012, 09:03 PM #3
Re: Rhoss CHiller problem
Apparently the clock card is faulty..
Alarm clock is damaged, clock card installed.
Press the ALARM, disable the unit back on. Assess the persistence of the alarm, a contacteréventuellement authorized service center and procéderau card replacement clock.
Cheers