    Rhoss CHiller problem



    Dear All

    I have a problem with Rhoss chiller model : CWA / E 185
    unit do not start and stopped at AL02

    I do not have any manual , alarm list
    please advice any manual will be usefull at : waseemnaamo@yahoo.com

    Regards



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Rhoss CHiller problem

    sorry no manual- check continuity of thr flow switch, then safety circuits pump contacts- hp,lp switch- displayed water temp compare with actual temp

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Rhoss CHiller problem

    Apparently the clock card is faulty..

    Alarm clock is damaged, clock card installed.
    Press the ALARM, disable the unit back on. Assess the persistence of the alarm, a contacteréventuellement authorized service center and procéderau card replacement clock.

    Cheers
    Stu