    Micro-Channel Condensers



    Any one have any experience with Micro-channel condensers? Either in new store applications or retro-fits? I had heard they had problems with leaks? Any reports would be appreciated.

    Thanks



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Micro-Channel Condensers

    I have been using them for some time as condensing coil.
    Never as evaporating.
    I'm quite happy with the technology. Good performance and helpful in reducing the refrigerant charge.

  3. #3
    Join Date
    Mar 2010
    Location
    usa
    Age
    46
    Posts
    120
    Rep Power
    17

    Re: Micro-Channel Condensers

    I had a Micro Channel condenser on a smaller Heatcraft Cond Unit with a problem. Some of the passes on the Condenser were restricted. This was a result of a system problem, but a Regular Condenser with 3/8" tubes would not have been pluged and the Nasty Stuff would have got caught in the Filter Drier. This was The only Problem on the 15 or so I have serviced.

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Micro-Channel Condensers

    Quote Originally Posted by THE DUDE View Post
    I had a Micro Channel condenser on a smaller Heatcraft Cond Unit with a problem. Some of the passes on the Condenser were restricted. This was a result of a system problem, but a Regular Condenser with 3/8" tubes would not have been pluged and the Nasty Stuff would have got caught in the Filter Drier. This was The only Problem on the 15 or so I have serviced.
    Interesting feedback.

    Could blockage perhaps be managed with a filter prior to condenser entry, for these systems?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Mar 2010
    Location
    usa
    Age
    46
    Posts
    120
    Rep Power
    17

    Re: Micro-Channel Condensers

    Quote Originally Posted by desA View Post
    Interesting feedback.

    Could blockage perhaps be managed with a filter prior to condenser entry, for these systems?
    Yes but on smaller systems it dosent seem cost feasible from the MFG standpoint. On larger Rack systems with a Microchannel Condenser I would definitely spec a Coalescent Oil Seperator ( Temprite)