Results 1 to 10 of 10
    Jul 2012
    buffalo ny
    1
    150 ton trane screw chiller
    Hey guys,
    I have a 150 ton trane screw chiller that has been going off on some oil faults. There are a bunch of ports on the compressors to connect gauges to, however none are labeled and trane is of no help. They will not give up the information, they send me some bull $hit manual tnat tells you nothing. Does anyone have experience with this machine? Its a. Rtac 150
    Thankyou in advance
    Mike
    Apr 2009
    israel
    778
    Re: 150 ton trane screw chiller
    what are these fault codes?
    the chiller should discribe what kind of fault this is?
    low oil flow?loss of oil?
    once you tell us what the nature of these faults are you will get more responses!
    if you mail me i will send you the relevant manual..
    good luck
    Jun 2012
    india
    44
    7
    Hi guys,
    Can u explain exact diagnostic it is high oil temp or low oil flow.so we will defenetly help to you also send your email id will send the manual.
    manchester
    5,639
    http://www.mediafire.com/view/?ai8zwflpc99wilz
    page 70 shows port connections on compressor- also shows how to check the oil level too
    Jun 2012
    india
    44
    7
    i am lookind for trane spare parts do you know where i get.
    manchester
    5,639
    trane.....
    Quote Originally Posted by tarunenrser58 View Post
    Jul 2012
    Usa
    The original post by miked123 was posted in regards to the machine I am working on.
    The machine is a Trane Rtac-155 with remote evaporator. In the diagnostic history the unit had a code of 198 "low oil flow". However, after starting the machine up, I have yet to have that error duplicate. I have had error codes 6b3 "low evap temp" and error
    Code 8a "evaporator water flow ( high approach temperature )" these codes shut the unit down on three attempts to start. On the fourth attempt the machine came online and continued to run without trouble. I am wondering why at initial start-up this issue was present.
    4,706
    Hi Johnny
    The plot thickens!
    Maybe you had some initial cavitation or gas pockets which have now cleared?
    Who knows!
    All well that ends well eh!
    Jul 2012
    Usa
    A high fives to install monkey for that manual. That was a huge help in regards to oil level assessment. Thanx for that!! Grizzly - the machine is a runn'in... We will see what today brings....!
    Jul 2012
    Usa
    Turned out the unload solenoid on compressor 2A was not functioning properly due to the coil of solenoid was not fully seated on shaft of solenoid. Chiller is up and runn'in...