Results 1 to 9 of 9

Thread: oil traps

  1. #1
    Join Date
    Jul 2012
    Location
    uk
    Age
    42
    Posts
    3
    Rep Power
    0

    oil traps



    what is the limit of oil traps u can have on a vrf with 26 fancoils and if there is to many traps will this damage the compresser



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: oil traps

    .

    Some have no oil traps. Others do, depends on the height differance
    and the location of the evaps compared to the compressor. it also
    varies between manufactures

    The only true way to know would be to use the manufacturers instructions
    because too many may, amongst other problems cause a pressure
    drop along the suction line. Plus more traps = more oil inside the system.

    Regards

    Rob

    .

  3. #3
    Join Date
    Jul 2012
    Location
    uk
    Age
    42
    Posts
    3
    Rep Power
    0

    Re: oil traps

    will this lead to the compresser burning out or shortin the life of the compressor

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: oil traps

    look at instal manual or check with tecnical be for instaling oil traps

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: oil traps

    Quote Originally Posted by dominic kiely1 View Post
    will this lead to the compresser burning out or shortin the life of the compressor

    Short answer: YES.

    Longer answer:
    To the best of my knowledge none of the big VRV/VRF manufacturers endorse oil traps.
    However, each oil trap added to the system will require a certain amount of oil and as there is a limited amount of oil in the system the oil to "feed" the traps has to be taken from somewhere else within the system, after all the oil has disappeared from the compressor the compressor will stop working.



    .

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: oil traps

    Most if not all VRF systems have very efficient oil separators and the refrigerant velocity is sufficient for oil return from the field pipe work providing the installation is up to scratch.
    I personally never have or never would consider oil traps on a VRF installation unless advised to do so by the bloke who design's the kit for the manufacturer...
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: oil traps

    none on vrv vrf-highcool splits and airedale and imi recommend oil traps- as long as your kit is installed within the install parameters- maximum total piperun, max height between indoor.outdoor, distance between 1st and last indoor- all will be ok , as stu says they have oil seperators-and some kit does an oil return mode-(tosh)
    Quote Originally Posted by dominic kiely1 View Post
    what is the limit of oil traps u can have on a vrf with 26 fancoils and if there is to many traps will this damage the compresser

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: oil traps

    Quote Originally Posted by dominic kiely1 View Post
    will this lead to the compresser burning out or shortin the life of the compressor
    Dom. It reads as though you have a specific point or problem and want
    a specific answer?

    If you gave us some more information about the system then
    we could answer with a more specific answer.

    But what has been said is as good as you will get with
    the limited information you have given.

    Regards

    Rob

    .

  9. #9
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: oil traps

    Quote Originally Posted by dominic kiely1 View Post
    what is the limit of oil traps u can have on a vrf with 26 fancoils and if there is to many traps will this damage the compressor
    As small number as possible, zero will be much better. Oil is lube for compressor and must return back to compressor no matter how, lack of oil will damage the compressor.

    Some said, oil traps will shorten the life of compressors as follows:
    No. of oil trap >> Life of compressor
    one or zero >> 10 years
    two to 5 >> 1 years
    5 or more >> 3 months
    10 or more >> 3 hrs
    15 or more >> 3 mins