Thread: Bitzer gasket
14-12-2005, 03:50 PM #1
Bitzer gasket
We have chiller with Bitzer compressors and resantly we found broken gasket betwen high side of valve plate and lov side.The gasket is all burn out.Evereting sims normal 3 days ago the suction pressure 3,1 bar gauge,discharge pressure 18,6 bar gauge.Subcooling 3 C,superheat on suction 8 C,superheat on discharge 25.Current is normal and voltage to.(R 407C ,BSE 32 oil)
Did someone find something similar on Bitzer compressor.
renato
14-12-2005, 07:20 PM #2
Re: Bitzer gasket
If it's the smallest piece on the gasket between LP and HP, then it's many times due to pumping of non compressibles (oil or refrigerant) which occurs sudden for some reason.
The Prestcold's and older DWM's had many times the same failure.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
14-12-2005, 08:08 PM #3
Re: Bitzer gasket
Hi I have a carlye compressor that was tripping on oil pressure,also the discharge from the compressor was only warm.I removed one of the head to find the gasket between the head and valve plate to be very brittle and broken.I changed the valve plates and gaskets and the compressor work well for about 24 hrs but now it trips on oil every 2 hours.Would this be for the same reason.
Regards Bernard
16-12-2005, 09:05 PM #4
Re: Bitzer gasket
Originally Posted by bernard
Steve
03-11-2010, 07:00 PM #5
Re: Bitzer gasket
Normally if you will have broken gasket at the discharge is it is pumping liquid refrigerant instead of gas or oil. did you check your valve plates? or you have tx valve into the unit which is flooded so liquid is coming back to the compressor.
04-11-2010, 10:08 AM #6
Re: Bitzer gasket
that post is 5 years old
Bitzer Octagon compressors
By RONB in forum Supermarket RefrigerationReplies: 25Last Post: 31-10-2010, 08:33 AM -
Bitzer s6f30 2-stage compressors
By JONAH in forum Technical DiscussionsReplies: 25Last Post: 27-10-2010, 07:27 AM -
Blown Discharge Gasket
By nh3wil in forum Industrial CompressorsReplies: 5Last Post: 22-08-2006, 04:59 PM -
Bitzer 8FC70.2
By Renato RR in forum CommercialReplies: 0Last Post: 18-07-2006, 11:46 AM -
Bitzer compressors
By Guy Hodgins in forum Trouble ShootingReplies: 1Last Post: 18-03-2004, 03:03 PM