    Exclamation Bitzer gasket



    We have chiller with Bitzer compressors and resantly we found broken gasket betwen high side of valve plate and lov side.The gasket is all burn out.Evereting sims normal 3 days ago the suction pressure 3,1 bar gauge,discharge pressure 18,6 bar gauge.Subcooling 3 C,superheat on suction 8 C,superheat on discharge 25.Current is normal and voltage to.(R 407C ,BSE 32 oil)
    Did someone find something similar on Bitzer compressor.

    renato



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Bitzer gasket

    If it's the smallest piece on the gasket between LP and HP, then it's many times due to pumping of non compressibles (oil or refrigerant) which occurs sudden for some reason.
    The Prestcold's and older DWM's had many times the same failure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Bitzer gasket

    Hi I have a carlye compressor that was tripping on oil pressure,also the discharge from the compressor was only warm.I removed one of the head to find the gasket between the head and valve plate to be very brittle and broken.I changed the valve plates and gaskets and the compressor work well for about 24 hrs but now it trips on oil every 2 hours.Would this be for the same reason.

    Regards Bernard

  4. #4
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23

    Re: Bitzer gasket

    Quote Originally Posted by bernard
    I changed the valve plates and gaskets and the compressor work well for about 24 hrs but now it trips on oil every 2 hours.Would this be for the same reason.

    Regards Bernard
    The main reason I found the Carlyle comps running on R408A I looked after doing that was because the oil suction strainer was clogged. Used to clog up over an hour or so, and then trip. Then if left to stand, some of the dirt would fall off, and the machine would be able to be reset and then start ok for another hour or two. Eventually, the strainer screen would tear, and new ones cost plus VAT.

    Steve

  5. #5
    Join Date
    Mar 2006
    Location
    Philippines
    Posts
    35
    Rep Power
    0

    Re: Bitzer gasket

    Normally if you will have broken gasket at the discharge is it is pumping liquid refrigerant instead of gas or oil. did you check your valve plates? or you have tx valve into the unit which is flooded so liquid is coming back to the compressor.

  6. #6
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Bitzer gasket

    that post is 5 years old

Similar Threads

  1. Bitzer Octagon compressors
    By RONB in forum Supermarket Refrigeration
    Replies: 25
    Last Post: 31-10-2010, 08:33 AM
  2. Bitzer s6f30 2-stage compressors
    By JONAH in forum Technical Discussions
    Replies: 25
    Last Post: 27-10-2010, 07:27 AM
  3. Blown Discharge Gasket
    By nh3wil in forum Industrial Compressors
    Replies: 5
    Last Post: 22-08-2006, 04:59 PM
  4. Bitzer 8FC70.2
    By Renato RR in forum Commercial
    Replies: 0
    Last Post: 18-07-2006, 11:46 AM
  5. Bitzer compressors
    By Guy Hodgins in forum Trouble Shooting
    Replies: 1
    Last Post: 18-03-2004, 03:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •