    Seemingly wrong PT relationship



    Hi.

    I have this 28 oz can of r410a at room temperature of 77F.
    When I connect a gauge to it, I measure 258 psig.
    The r410a PT chart says I should have 226 psig at 77F.

    What am I missing?

    Thanks.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Seemingly wrong PT relationship

    The compariter - PT chart is correct so.

    Either

    Your gauge
    Your thermomiter
    or
    The refrigerant is out.

    If you thermomiter and gauge is ok you do not have R410A.

    410 is a Zeotrope and it will fractionise (seperate) if it has had a
    leak in the past or if the thing was vented.

    I personaly would check my gauges and thermomiter for accuracy.

    Regards

    Rob

    .

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Seemingly wrong PT relationship

    Did you measure the vapour or liquid temperature?

  4. #4
    Join Date
    Jun 2012
    Location
    Canada
    Age
    64
    Posts
    2
    Rep Power
    0

    Re: Seemingly wrong PT relationship

    I measured the liquid temp, because I put my probe below the line. That is, as far as I can guess where the line is inside an opage can filled at 80% capacity.

    Thanks all for your time.