    CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout



    Hi Guys, I have a problem with Climaveneta Necs/B0352.

    1. I switched on the unit
    2. First Fan attempted to turn on and after about 5 seconds stopped and I saw Alarm 251 on the W3000 Compact
    3. Then it was the same with circuit 2 and i had Alarm 252


    Alarm 251 Circuit 1 start-up timeout Possible start-up attempt with no ***** in circuit 1.

    Alarm 252 Circuit 2 start-up timeout "as above, for circuit 2.

    When I manually turn on compressor it goes to 33 bars on delivery side and turn off.

    What do You think, What is the cause of these alarms? At the moment i can't check if there is refrigerant because i don't have recovery station.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout

    You forgot a shut off valve closed, or nitrogen in the system.

  3. #3
    Join Date
    Jul 2012
    Location
    Poland
    Age
    32
    Posts
    3
    Rep Power
    0

    Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout

    Thanks for Your reply.
    So in Your opinion there is refrigernat, yes?
    In relation to shut-off valve, should i close it using user interface or manually?
    Could You tell me more about nitrogen in the compressor? How can i check nitrogen in the system?

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout

    Hi
    what we are trying to tell you here is that the units controller doesnt see any pressure change in the low transducer,you should have a ref tech check the unit ,attemting to run the unit with no ***** will harm your comps !!
    is this a new unit or a old one??
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout

    Quote Originally Posted by adamski View Post
    Thanks for Your reply.
    So in Your opinion there is refrigerant, yes?
    In relation to shut-off valve, should i close it using user interface or manually?
    Could You tell me more about nitrogen in the compressor? How can i check nitrogen in the system?
    Ok, stop there before anyone gets hurt or the chiller fails, and call a refrigeration engineer.

  6. #6
    Join Date
    Jul 2012
    Location
    Poland
    Age
    32
    Posts
    3
    Rep Power
    0

    Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout

    It's quite new unit- 2008
    In this week i will have a recovery station