01-07-2012, 09:59 AM #1
CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout
Hi Guys, I have a problem with Climaveneta Necs/B0352.
1. I switched on the unit
2. First Fan attempted to turn on and after about 5 seconds stopped and I saw Alarm 251 on the W3000 Compact
3. Then it was the same with circuit 2 and i had Alarm 252
Alarm 251 Circuit 1 start-up timeout Possible start-up attempt with no ***** in circuit 1.
Alarm 252 Circuit 2 start-up timeout "as above, for circuit 2.
When I manually turn on compressor it goes to 33 bars on delivery side and turn off.
What do You think, What is the cause of these alarms? At the moment i can't check if there is refrigerant because i don't have recovery station.
-
01-07-2012, 10:57 AM #2
Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout
You forgot a shut off valve closed, or nitrogen in the system.
-
01-07-2012, 11:38 AM #3
Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout
Thanks for Your reply.
So in Your opinion there is refrigernat, yes?
In relation to shut-off valve, should i close it using user interface or manually?
Could You tell me more about nitrogen in the compressor? How can i check nitrogen in the system?
-
02-07-2012, 08:15 AM #4
Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout
Hi
what we are trying to tell you here is that the units controller doesnt see any pressure change in the low transducer,you should have a ref tech check the unit ,attemting to run the unit with no ***** will harm your comps !!
is this a new unit or a old one??
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
02-07-2012, 09:02 AM #5
-
02-07-2012, 09:47 AM #6
Re: CLIMAVENETA NECS/B0352 Compressor is not working, Circuit 1&2 start-up timeout
It's quite new unit- 2008
In this week i will have a recovery station