    high pressure float valve



    My company need some high pressure float regulator,the refrigerant is R717,2200KW.Danfoss high pressure float valve capacity is not enough.Can anyone help me.



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: high pressure float valve

    Use two or more smaller valves in parallel. Pay attention to the orientation to the pipe work to allow for flow in / out of each.