Thread: Vacuum Tester
30-06-2012, 01:02 AM #1
Vacuum Tester
Easy vacuum tester. Never needs calibration. Water temp down to -18 deg C
I wonder how much that is in microns..
http://www.youtube.com/watch?v=9h_lv...&feature=g-upl
30-06-2012, 07:56 AM #2
Re: Vacuum Tester
we only see how vacuum freeze water for 0 degree C point - not how much below it.
0 degree C water (water/ice) = 6.1 mBar = 4570 micron
-10 degree C water (ice) = 2.599 mBar = 1950 micron
-18 degree C water (ice) = 1.27 mBar = 952 micron
(edit - missing multiply 1000 times on micron value in convension from mBar, this is corrected now)Last edited by xxargs; 01-07-2012 at 11:12 PM.
30-06-2012, 12:13 PM #3
Re: Vacuum Tester
Heyyy.... Thanks for that.
Can you tell me the formula you use to get to this figure.? That would be handy for me to know..
Cheers mate
Peter
01-07-2012, 11:01 PM #4
Re: Vacuum Tester
I take pressure value over water/ice from refprop, but possible source if you want formula, you can find here http://cires.colorado.edu/~voemel/vp.html - is not easy relation in simple formula and also many formula from different scientists author to select between - pick one you trust most :-)...
conversion between micron and mBar is easy
(micron/1000) * (1/0.75) = mBar
mBar * 0.75 * 1000 = micron
02-07-2012, 08:51 AM #5
Re: Vacuum Tester
Hi xxargs..
I clicked on that link and I think those formulas are very easy to understand. . . . . . . . . Not..... hehehe....
Thanks again mate... cheers
Peter