    Vulcan Lockring for R410a A/C system


    I have been brazing flare to solder connectors on my R410a installs as I've had too many problems with standard flares failing.
    Lugging a Oxy/Acetylene portapac round and all the hassle of hot work permits and safety rules etc sucks. I'm tempted by the Vulcan Lokring system... anyone used one... is it any good?



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Vulcan Lockring for R410a A/C system

    funnily enough this thought has been going round my mind recently as I've heard they can shed 40% install time off a vrv

    but are they any good??

    cheers

    richard

  3. #3
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    66
    Posts
    10,067
    Rep Power
    40

    Re: Vulcan Lockring for R410a A/C system

    I've used them in the past on R22 systems when installing in old wooden buildings without problems.

    You need to allow room to work but saves looking around the back of your brazes !!
    Brian - Torquay, Devon, UK
    I have to stop saying "how stupid can you be?" to my co-workers.
    They're starting to take it as a challenge...

    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    41
    Posts
    711
    Rep Power
    13

    Re: Vulcan Lockring for R410a A/C system

    I don't mean to dampen anybodys enthusiasm.....BUT!!!!

    A company i sometimes work for, bought this type of kit to try out, not sure what make it was.(but it would NOT have been a cheapo one)
    At least half of the joints failed on 410a.
    Just to make sure, a differant install team tried the kit and got the same result.
    That kit cost them a fortune, and they were not prepared to try it again.
    I can see if i can get it at a good price if anybody wants it only used on two jobs, one carefull owner etc etc etc
    I passed up the opportunity

    cheers

    eggs

  5. #5
    Join Date
    Nov 2005
    Location
    USA, New Jersey
    Age
    51
    Posts
    17
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    OK guys, so what the hell is a "hot work permit". Being from the US I have never heard this one before.

    Chill

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by chiller563
    OK guys, so what the hell is a "hot work permit". Being from the US I have never heard this one before.

    Chill
    if you go on a lot of sites in the UK you need a 'hot works permit' this is a safety assessment of the job you are about to do if it involves 'hot works' ie welding brazing etc.
    you will be req'd to show risk assessments and safety procedure plus extinguishers available time on site after all 'hot works' is finished etc etc

    cheers

    richard

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,340
    Rep Power
    16

    Re: Vulcan Lockring for R410a A/C system

    A hot work permit is required here in the US also in some applications. These are very standard requirements when working on ammonia refrigeration systems and are part of the PSM (Process Safety Management) programs.

    The permit is issued by the facility owner. It will list all of the requirements you are responsible for during "hot work" processes. The hot work processes include welding, brazing, cutting (with a torch or other spark producing device).

    The permit is valid only for the stated operation and must be returned to the client when the job is complete. The permit is recorded and signed off as complete.

    When you get into industrial refrigeration, refineries, or chemical plants the permit must be valid before you start work.

  8. #8
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,155
    Rep Power
    17

    Re: Vulcan Lockring for R410a A/C system

    Some years back I was called to a Shopping Mall..........The place I was working in was Coombes Bakery I think.

    I started welding...............Next thing..............Trrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrrring

    The whole................I mean whole centre was evacuated........

    The wail of fire engines sirens still haunt me......

    I realised it was Me..................but like a coward I slunk away to the basement.......

    When the dust had settled, they had looked at the control panel zones.........identified the location of the smoke detector......

    and found the offending welding gear............

    They were waiting for me.............

    That will rank as the most embaressing moment of my life,

    That is Why a hot permit is required

    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Angry Re: Vulcan Lockring for R410a A/C system

    I emptied out a 5* hotel at lunch time because the dectector was hidden

    I glanced around and not seeing a SD went ahead braised..oppsee doopsee :-/

    The thing was against the wall and a shelf that had been fitted right up to it. Even the maintenance men had trouble finding it.


    Cheers

    richard

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,722
    Rep Power
    29

    Re: Vulcan Lockring for R410a A/C system

    One of the universities where we work will pass on the 350 call out charge for the fire brigade to whoever is responsible for the false fire alarm - things we say to try and pass the blame
    I'm back on the Pale

  11. #11
    Join Date
    Sep 2005
    Location
    uk
    Age
    44
    Posts
    512
    Rep Power
    10

    Re: Vulcan Lockring for R410a A/C system

    A few years ago myself and a collegue emptied part of the ICI plant at runcorn, and emerged into the car park to be greeted by 2500 employees, 3 police cars, 4 fire engines and a fire investigation tactical unit. we were saved by the fact that the alarm klaxon in the basement where we were working was broken and we were at risk by the fact we heard no alarm. an expensive job for a 12000 an hour split a/c system (glad i did not foot the bill).
    Takes a licking, keeps on ticking.

  12. #12
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    48
    Posts
    768
    Rep Power
    12

    Re: Vulcan Lockring for R410a A/C system

    Managed to empty a call centre this Summer with the dust from my core borer upsetting the smoke detectors
    Karl

  13. #13
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    39
    Posts
    59
    Rep Power
    9

    Re: Vulcan Lockring for R410a A/C system

    Thanks for the info... what a choice! Either fork out for a Lokring set and risk expensive R410a leaks, or suffer the consequences of setting fire alarms off! Nightmare!

    As I thought, there's no easy way! Magic Just Magic!!

  14. #14
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,155
    Rep Power
    17

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by frank
    One of the universities where we work will pass on the 350 call out charge for the fire brigade to whoever is responsible for the false fire alarm - things we say to try and pass the blame
    They were going to fine me 500.00, but I put on such a pathetic sad face.... the bill never ever did arrive
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  15. #15
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    50
    Posts
    145
    Rep Power
    9

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by rbartlett
    if you go on a lot of sites in the UK you need a 'hot works permit' this is a safety assessment of the job you are about to do if it involves 'hot works' ie welding brazing etc.
    you will be req'd to show risk assessments and safety procedure plus extinguishers available time on site after all 'hot works' is finished etc etc

    cheers

    richard
    Sorry, how about installation for residential and open air at commercial buildings area too? Other than fire hazard industrial areas like refineries,phamacutical plants etc.

  16. #16
    rbartlett's Avatar
    rbartlett Guest

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by Cofreth
    Sorry, how about installation for residential and open air at commercial buildings area too? Other than fire hazard industrial areas like refineries,phamacutical plants etc.

    Eash site will have it's own set up and regulations. usually H.W.P only apply to the inside of the building but others will insist on a rsk assessment just in case. it's all very time consuming and my heart sinks when in -say- a large shopping centre and I see that some hot works is req'd

    cheers

    richard

  17. #17
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    As a new member and with over 10 years of technical support for the Lokring product< I would welcome any questions with regard to the Lokring product and its usage, The connector is suitable for R410a when applied correctly the working pressures are 50 bar with refrigeration grade Copper and a stated 200 bar burst.

  18. #18
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,068
    Rep Power
    15

    Re: Vulcan Lockring for R410a A/C system

    .



    Lockring Pete,

    How does this system of jointing stand when conformity with the PED is needed?

    Anybody come across a PED conformity assessment using this gear yet?

    .
    ________
    weed vaporizer
    Last edited by Argus; 07-02-2011 at 10:27 AM.

  19. #19
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,722
    Rep Power
    29

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by lokringpete View Post
    The connector is suitable for R410a when applied correctly the working pressures are 50 bar with refrigeration grade Copper and a stated 200 bar burst.
    And what are the probles encountered when the installation space is restricted and the lockring is not installed correctly? Do you have to rip out sections of pipe?
    I'm back on the Pale

  20. #20
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    39
    Posts
    59
    Rep Power
    9

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by lokringpete View Post
    As a new member and with over 10 years of technical support for the Lokring product< I would welcome any questions with regard to the Lokring product and its usage, The connector is suitable for R410a when applied correctly the working pressures are 50 bar with refrigeration grade Copper and a stated 200 bar burst.
    Hi Pete.
    Is there a UK base where the Lockring product could be viewed and demonstrated? Possibly, some of the problems are down to lack of training? Could this be addressed?
    I have continuous problems with HWP's etc, so if I could join R410 lines reliably and without heat then I'd buy a kit!

  21. #21
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    48
    Posts
    768
    Rep Power
    12

    Re: Vulcan Lockring for R410a A/C system

    I have a Vulkan Lokring set but all of my fittings are aluminium for use with automotive tubing though I did have the presence of mind to buy the larger ratchet so that it could be used for larger tubing. The problem that I have found with the alloy fittings is that they can lock up and go on crooked, this is mainly due to there being limited acess to automotive pipework but what it does do it does very well. The car makers do love to use unusual sized flexi pipe and alloy tubing which means that frequently there is no fitting to suit (My selection of fittings is pretty big) Really there should be no excuse for me not to use Vulkans as I too hate dragging bottles about and really....really hate messing around with long coils of semi hard tubing.
    Karl

  22. #22
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    The Lokring has been tested by many independent bodies such as Lloyds,UL and TUV and is certified by these bodies as to the working and burst pressures.
    I hope that this answers your question if not please advise the criteria that you need to satisfy and I will do my best to give you the relevant in formation.

  23. #23
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by frank View Post
    And what are the probles encountered when the installation space is restricted and the lockring is not installed correctly? Do you have to rip out sections of pipe?
    The Lokring connector is a permanent joint and if installed incorrectly it would require cutting out.
    New tooling has been developed to try to assist with tight working areas and the assembly instructions have now been simplified to ensure that mistakes by the user are kept to an absolute minimum.

  24. #24
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by daddymac View Post
    Hi Pete.
    Is there a UK base where the Lockring product could be viewed and demonstrated? Possibly, some of the problems are down to lack of training? Could this be addressed?
    I have continuous problems with HWP's etc, so if I could join R410 lines reliably and without heat then I'd buy a kit!
    Vulkan Lokring have an office in Brighouse and they have engineers that would be happy to demonstrate the working proceedures and tooling.
    If you require any further details drop me a message.

  25. #25
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by Argus View Post
    .



    Lockring Pete,

    How does this system of jointing stand when conformity with the PED is needed?

    Anybody come across a PED conformity assessment using this gear yet?

    .
    Re: Vulcan Lockring for R410a A/C system
    The Lokring has been tested by many independent bodies such as Lloyds,UL and TUV and is certified by these bodies as to the working and burst pressures.
    I hope that this answers your question if not please advise the criteria that you need to satisfy and I will do my best to give you the relevant in formation.

  26. #26
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,722
    Rep Power
    29

    Re: Vulcan Lockring for R410a A/C system

    Can the Lockring, say, be used to install a replacement reversing valve into an air cooled condensing unit?
    I'm back on the Pale

  27. #27
    Join Date
    May 2004
    Location
    New Zealand
    Age
    60
    Posts
    11
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by rbartlett View Post
    I emptied out a 5* hotel at lunch time because the dectector was hidden

    I glanced around and not seeing a SD went ahead braised..oppsee doopsee :-/

    The thing was against the wall and a shelf that had been fitted right up to it. Even the maintenance men had trouble finding it.


    Cheers

    richard
    I did the same at Marks and Sparks in Wolverhampton !! Didnt tell them I was doing a braze, and bingo all hell was let loose. I kept my head low all that week.

  28. #28
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by frank View Post
    Can the Lockring, say, be used to install a replacement reversing valve into an air cooled condensing unit?
    Lokring do have machined flare connections for this purpose which have a copper bonnet washer to seal between the flare faces with a half Lokring joint to connect to the pipe.

  29. #29
    Join Date
    Oct 2006
    Location
    west sussex
    Posts
    6
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Hi, i used lockrings on an install last year to install several toshiba rav1400s, pressure testing was fine but when the system went into heating we started to have leaks this i belevie was caused by the fittings expanding at a different rate to the pipe as the lockrings are quite a heavy brass. i called lockring out to site and there advise was to use a pipe liner on all pipe wall thicknesses, this i did and at the momet have not had a problem.one thing i will say is do not use there euro fittings / flare as they cannot stand being taken of and re tightend, they will leak
    Al

  30. #30
    Join Date
    Oct 2006
    Location
    UK
    Age
    48
    Posts
    168
    Rep Power
    8

    Re: Vulcan Lockring for R410a A/C system

    Hello All,

    Just joined this site.

    I had some experience of this lockring at Heathrow Airport. The installer had to use this as they could not get a hot work permit. The kit was a Daikin super multi plus with the BP Boxes (branch providers). On first start up they found that the 3 out of 4 indoor units did not cool, checked the obvious cross wiring/piping, refrigerant leaks but could not find the problem. It looked as if the EEVs in the BP boxes were not opening. Replaced the PCB in the BP box then the EEV motor, then the whole BP box. Still could not find the problem. In the end ended up cutting all the pipes to find total blockages where the lockring fittings were fitted. The copper pipe need to be coated in some kind of a epoxy resin before the brass lockring is compressed on. Somehow the installed managed to get large amounts of resin inside the copper pipes. Even found a blockage in a middle of the pipe between two lockring fittings.

    The main question we had was, how does the resin react with the refrigerant and the oil?
    Brazing can be a pain, but is proven!!

    Obi Wan

  31. #31
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by alsmc View Post
    Hi, i used lockrings on an install last year to install several toshiba rav1400s, pressure testing was fine but when the system went into heating we started to have leaks this i belevie was caused by the fittings expanding at a different rate to the pipe as the lockrings are quite a heavy brass. i called lockring out to site and there advise was to use a pipe liner on all pipe wall thicknesses, this i did and at the momet have not had a problem.one thing i will say is do not use there euro fittings / flare as they cannot stand being taken of and re tightend, they will leak
    Al
    The inserts are required with all soft tubes 3/8" od and above, this provides the joint with added security in the event that the tube is moved after assembly, however I would personally suggest that an insert is used on all tubes with a wall thickness of 1mm or less for added security against tube movement during an installation.

    I was interested to note your comments with regard to the euro fittings and would like to know the torque settings used when tightening the flares so we can establish your findings.

  32. #32
    Join Date
    Sep 2006
    Location
    England
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by Obi Wan View Post
    Hello All,

    Just joined this site.

    I had some experience of this lockring at Heathrow Airport. The installer had to use this as they could not get a hot work permit. The kit was a Daikin super multi plus with the BP Boxes (branch providers). On first start up they found that the 3 out of 4 indoor units did not cool, checked the obvious cross wiring/piping, refrigerant leaks but could not find the problem. It looked as if the EEVs in the BP boxes were not opening. Replaced the PCB in the BP box then the EEV motor, then the whole BP box. Still could not find the problem. In the end ended up cutting all the pipes to find total blockages where the lockring fittings were fitted. The copper pipe need to be coated in some kind of a epoxy resin before the brass lockring is compressed on. Somehow the installed managed to get large amounts of resin inside the copper pipes. Even found a blockage in a middle of the pipe between two lockring fittings.

    The main question we had was, how does the resin react with the refrigerant and the oil?
    Brazing can be a pain, but is proven!!

    Obi Wan
    The Lokprep solution is compatible with all refrigerants and the correct amount of Lokprep is stated in the instructions as:

    5)Apply sufficient Lokprep to form a continuous bead around the tube circumference to ensure a good coating thus ensuring all surface imperfections are sealed within the Lokring joint.

    I would welcome the opportunity to show you the correct
    application of a Lokring connector as proven tube jointing
    technique as I am sure that it would prove beneficial for this
    type of application if applied by a competent engineer.

  33. #33
    Join Date
    Oct 2006
    Location
    UK
    Age
    48
    Posts
    168
    Rep Power
    8

    Re: Vulcan Lockring for R410a A/C system

    Dear Lockringpete,

    Thanks for the invite, but I am unlikely to use it myself. Can you send me the technical data or URL. People are always asking me about this.

  34. #34
    Join Date
    Mar 2006
    Location
    Spain
    Posts
    23
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Hi all I have been using lokring fittings on splits and multi spits in Spain for ages, just follow the instructions and use the correct tools and they work great,

    I was trying to reply to this thread with a link for a PDF to show all the lokring fittings, tools and user guide but wont let me post the link if anybody wants it you can email me and I will let you have it,


    clivo

  35. #35
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    56
    Posts
    203
    Rep Power
    8

    Re: Vulcan Lockring for R410a A/C system

    Hi all, I have been using the lokring fittings on splits and multis for a good while now with no problems. pressure tested to 40 bar for 48hours on several occassions with no sign of a leak.

    As long as you fit the inserts to soft drawn pipe there should be no problem. It is saving me hours of wasted time getting brazing permits, shutting off fire alarms and the inevitable staying on for at least an hour for fire watch.

    Also most liability insurance policies now require a second operative to be present during hot work. They must not be involved with the work being carried out and are there purely to raise the alarm or operate the fire extinguisher if the worst should happen. Now I can safely join pipes on my own.

    Personally I think it is a great bit of kit.

    Graham

  36. #36
    Join Date
    Sep 2005
    Location
    South West
    Age
    41
    Posts
    131
    Rep Power
    9

    Re: Vulcan Lockring for R410a A/C system

    Has anyone had any problems with using the Lokring system with branch valves. Am think about changing form brazing due to the permits etc? Thanks

  37. #37
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,068
    Rep Power
    15

    Re: Vulcan Lockring for R410a A/C system

    I'd strongly urge you to check if this type of joint method will be acceptable to your client as an alternative to brazing.

  38. #38
    Join Date
    Jan 2007
    Location
    London
    Posts
    2
    Rep Power
    0

    Talking Re: Vulcan Lockring for R410a A/C system

    Hey I have been using vulcan lockring joints for 2 years and find them brilliant if you take your time and prepare the joint properly by cleaning with emery cloth then wipe off dust and use lockprep fluid.

    only ever messed up 2 joints out of dozens
    Hope this helps

  39. #39
    Join Date
    Nov 2006
    Location
    India
    Posts
    12
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Dear Friends
    I am in Domestic Refrigerator Manufacturing Company
    I have taken up project for converting Brazing Joints to Lock Ring Joints

    At present we are using 25% Silver Rods for copper to Steel Joints and 2% Silver Rods for Copper to Copper Joints

    We have planned to change Copper -Steel joints ( 25% Silver ) to Lock rings for cost benefits

    Can you help me in let me know the benefits of Lock rings over Brazing Joints in terms of
    1. Reliability,
    2. Consistency in quality,
    3. Skill require,
    4. Cost
    5. Production rate

  40. #40
    Join Date
    Aug 2007
    Location
    england
    Posts
    26
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    ive been using the lokring kit on R134a auotmotive pipe repairs.....no failures yet....access is the only problem as you need a bit of space to work the pliers.

  41. #41
    Join Date
    Aug 2007
    Location
    Philippines
    Posts
    2
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Hi Guys!

    That was very funny and embarashing experience about "hot work permits" and SD incidence... I will always remember that..

    Thanks.

  42. #42
    Join Date
    Jul 2006
    Location
    uk
    Posts
    7
    Rep Power
    0

    Post Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by eggs View Post
    I don't mean to dampen anybodys enthusiasm.....BUT!!!!

    A company i sometimes work for, bought this type of kit to try out, not sure what make it was.(but it would NOT have been a cheapo one)
    At least half of the joints failed on 410a.
    Just to make sure, a differant install team tried the kit and got the same result.
    That kit cost them a fortune, and they were not prepared to try it again.
    I can see if i can get it at a good price if anybody wants it only used on two jobs, one carefull owner etc etc etc
    I passed up the opportunity

    cheers

    eggs
    Hi Please contact a local wholesaler to do free trading how to use the kit and you will have no more problems it is all about preparing the pipe and possible that you needed the inserts if the pipe was not the right gauge
    regards ice ken

  43. #43
    Join Date
    Apr 2007
    Location
    england
    Age
    32
    Posts
    22
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    We have just got 1 of these kits. Dont know when ill use it but I will let you know how it goes.

  44. #44
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    5
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Hello there,

    Vulcan Lockring.......

    We use them on R600a fridge work, never used them on A/C units.

    The problem with using Lockring on fridge units is the total lack of space for the grips.

    However, when used correctly, the joints rarely leak. The secret I am told is correct use of/applying liberal amounts of fluid.

    Where possible we braze and only use the kit where obtaining a HWP is difficult. For example Airports etc.

    Hope this helps?

    Trev.

  45. #45
    Join Date
    Jul 2007
    Location
    South Africa
    Posts
    4
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Hi Guys

    I used to work for a company here in South Africa and we did an installation with the Mitsubishi City Multi 410a . The Loc-ring system was utilised, the joint held together during the pressure test , but when the units were commisioned we started experincing disasterous failures of the joints. At the end of the day we had to cut out all of the joints and use the standard brazed fittings. They did how ever admit that was a manufacturing fault in the fittings. I would not recomend them at all.

  46. #46
    Join Date
    Jul 2007
    Location
    Sussex
    Age
    32
    Posts
    33
    Rep Power
    0

    Smile Re: Vulcan Lockring for R410a A/C system

    Hi,
    We only use lokring now and have never had a problem with using it on R410a, it is quick and very easy to use and just speeds the whole install job right up - on a downer last year we got a dodgy batch of 3/8 lokrings, put 4 in on a job and all leaked on pressure test, took them all out replaced all and again all leaked - not happy! but we sent them all back to lokring who apologised and replaced the lot - since then not had a problem since.
    Would def recomment using it.
    Paul

  47. #47
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    89
    Rep Power
    7

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by FrankA View Post
    Hi Guys!

    That was very funny and embarashing experience about "hot work permits" and SD incidence... I will always remember that..

    Thanks.
    Been there and done it myself with building evacs , the worst was a high rise with 50 hp main fan it stopped due to a speed drive fault, i checked out the motor and restarted it and it went up in smoke in the air handler , i felt like a **** when 13 levels of office block was being emptied , then my next was i shifted a tile and didnt realise the retard fire alarm guys not only ran the wires in .75 mm single core but also just threw the cable from detector to detector over the tiles, i wasnt even close to a detector and managed to pull a wire and set off the alarms, then i was donig a repair on a york water chiller and did all the right things got a hot work permit , got the fire guys out to isolate everything , started the weld then the alarms went off , standing outside the firemen somehow knew who to see and even knew my name , ends up someone who got sent an email smelled smoke and tripped a call point , the fire alarm guy said everything was isolated so i pointed the firemen in his direction , hey live and learn 17 years on the job you can expect ****ups

  48. #48
    Join Date
    Mar 2007
    Location
    USA
    Posts
    121
    Rep Power
    8

    Re: Vulcan Lockring for R410a A/C system

    Hey LokringPete,

    These gizzmos look interesting. The website has some videos to view but they are in some bizarro file format, so can't watch'em... Can an IT person at Vulcan upload those videos in the more common .mpg or .avi format???

  49. #49
    Join Date
    Jan 2008
    Location
    Spain
    Age
    49
    Posts
    2
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    Quote Originally Posted by Clivo View Post
    Hi all I have been using lokring fittings on splits and multi spits in Spain for ages, just follow the instructions and use the correct tools and they work great,

    I was trying to reply to this thread with a link for a PDF to show all the lokring fittings, tools and user guide but wont let me post the link if anybody wants it you can email me and I will let you have it,


    clivo
    Hi Clivo
    This is my first ever message on any forum so I hope it works!! !! I am living in Alhaurin and am in desperate need of Lokring stuff!!
    Specifically an aluminium step down from 7 to 6 for a domestic fridge. ( 7-6NRAL00 )
    Where do you buy?

  50. #50
    Join Date
    Jan 2008
    Location
    ptolemaida
    Age
    33
    Posts
    16
    Rep Power
    0

    Re: Vulcan Lockring for R410a A/C system

    take a mapp gas burner my friend and sold the inside unit connections,the cheapest and best!

Page 1 of 2 12 LastLast

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13