Results 1 to 5 of 5
  1. #1
    rajuafs's Avatar
    rajuafs Guest

    Identifying R404A



    Gents,
    How can anyone identify whether the refrigerant supplier has supplied genuine refrigerant
    R404a?

    Please help me.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Identifying R404A

    .

    Use the pressure temperature relationship test.

    At any given temperature the refrigerant will be at a certain pressure.

    Measure the temperature of the cylinder, measure the pressure of the
    cylinder and they should corrispond with what it should be on a chart
    or comparitor.

    Regards

    Rob

    .

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Identifying R404A

    thats the only way i know,why do you ask the question if you doubt your supplier find another not worth the risk!!

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Identifying R404A


  5. #5
    Join Date
    May 2012
    Location
    iraq
    Age
    65
    Posts
    11
    Rep Power
    0

    Re: Identifying R404A

    normaly for cooling down to 0C. the suction pr = 50, discharge pr = 300 psi.