    max operating temperature



    HI guys

    would anyone of you technical experts out there have an idea on the maximum operating temp of R22 and R410A say if the ambient temp were to get to 55 degrees C your input would be most welcome


    I can fix broke but I cant fix stupid :)

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: max operating temperature

    Been to 50C, hard to breath, burn your lungs, cooling units just running, you'll have to wait and see, I think they will survive it, just.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: max operating temperature

    Check a PT chart for temp/pressures.

    Check MSDS sheet for critical temperatures.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    pyro45686's Avatar
    pyro45686 Guest

    Re: max operating temperature

    itd be getting pretty close to your HP cut out i think. R22 lines up to 1840kpa at 50*c on my PT chart and r410 lines up with 2960kpa at 50*c. and condensing temp need to be higher by at least (?)15*C(?) on top of ambient so you get a plenty of liquid

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: max operating temperature

    .

    Most air cooled systems are sized to have about 15 degC temp differance
    above ambient temps.

    So if the ambient was at 40 degC the the condensing temp would be about 55 degC.

    The critical temp for R22 is 96 degC and R410 is 74degC.

    On paper that reads as 81 degC and 59 degC respective ambients.

    But the ststems would not tolerate that.
    It is higher than EN 378 pressure test standards for those refrigerants.

    I would say R22 does not want to be much above 22barg or about 40degC
    and R410A does not want to be above 34 barg.

    But as others have said they may run higher.

    Regards

    Rob

    .

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: max operating temperature

    Si

    Get the Bitzer app for your phone, as Rob says critical temps are very close to your ambient, there is bugger all you can do about the temperature but it would be feasible to replace the charge when it cools down, at those temps you must have issues with refrigerant breakdown?

    Al
    Mostly found in the southern part of this green and pleasant land.