    MTA chiller HP swicth fault



    Guy's

    Got an MTA chiller with two circuits. Went to site today and found both on HP switch fault. tried to reset but that didn't work. Tried cutting the Hp wire out and fault still there. I then removed the trip cable from the slave unit and it still no workie.
    DSC04460.jpg
    DSC04459.jpg

    Any ideas??
    Last edited by r.bartlett; 27-06-2012 at 05:36 PM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: MTA chiller HP swicth fault

    setting 3112 reset alarm -select yes then the alarm symbol will reset
    carel pco outstation- the programming is the same between manufacturers- airedale/lennox

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: MTA chiller HP swicth fault

    Quote Originally Posted by install monkey View Post
    setting 3112 reset alarm -select yes then the alarm symbol will reset
    carel pco outstation- the programming is the same between manufacturers- airedale/lennox
    more detail please as the carel tech guy said press alarm twice.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: MTA chiller HP swicth fault

    from the front screen press prog twice then select settings3 then general1 then order1 then select 2 al reset then highlight yes,enter the display will show yes then revert to no after 3 seconds and the red alarm light should dissappear
    pressing the alarm button twice will only give info of the cause of alarm and time

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: MTA chiller HP swicth fault

    check ur emails

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: MTA chiller HP swicth fault

    Had a discussion with MTA UK (for some reason I thought it was ICS and we all know how rubbish their tech 'help' is)

    Anyway had a chat and he emailed me a WD. with his help I knew roughly where I needed to look. I remembered I didn't have any voltage in/out of the HP so started to trace back.

    Turns out fuse on transformer had blown which -should- mean every alarm but only these two

    Anyway I had a small glass fuse and stuck that in. Water came down from 28.7 to 12,3 in 20 minutes with building on full cooling so plenty of capacity

    Hopefully that will see us through for now but must wonder why the thing blew in the first place

    Richard