Anyone aware of condenser coil issues on these units, suspect i've got a leaking one, pain in the arse to leak test.....
J
26-06-2012, 10:15 PM #2
Re: Daikin RYP100L7W1 R407c
had rzq100 cond coil go on 410a condenser- bottom row right behind cond fan bracket-you have to cut the fins away-managed to blob it- still working 4 mths later!
26-06-2012, 10:22 PM #3
last pic is all boxed up good to go
27-06-2012, 09:11 PM #4
failed another daikin today with a failed condenser coil..... theyve got me going to a daikin vrv on friday for a leak, suspected coil again....
27-06-2012, 10:13 PM #5
vrv's refnets split if the pipework is clamped too tight- also valve caps on the shut off valves-if not tight can leak- not schraeder caps!- when degassing if any in,vaccing and pressuretesting- drive all valves open on outdoor pcb
28-06-2012, 07:35 AM #6
28-06-2012, 07:37 AM #7
28-06-2012, 02:37 PM #8
Monkeys on to that- patch the coil,repair get overtime. Quote for new coil as customer is too tight to accept my other quote -so he will accept the quote for coil replacement ,hey presto comission and overtime- monkey wins!!!