hi from greece.i have a vector 1500 and he works with 50 psi low pressure and 410 the high pressure .any ideas about that .the temp go down very slow .the out temp is 38c celcious.thank.
-
25-06-2012, 11:12 PM #2
Re: carrier vector 1500 high pressure 410 psi
clean the condensor and take the front doors off.
-
26-06-2012, 11:05 PM #3
Re: carrier vector 1500 high pressure 410 psi
i do it and nothink change .maybe if i dont make good vacum in system.how can i do it?thanks.
-
26-06-2012, 11:07 PM #4
Re: carrier vector 1500 high pressure 410 psi
have anyone a manual for this unit.thanks
-
27-06-2012, 12:00 AM #5
Re: carrier vector 1500 high pressure 410 psi
has this unit got any history of being recharged recently if yes then it may have been wrongly charged,recover gas and vac it for 24 hours and recharge to the amount on the data plate[in liquid only,what happens when you put it thru a pretrip?
-
27-06-2012, 05:26 PM #6
Re: carrier vector 1500 high pressure 410 psi
he has one fault a127 check sct sensor .the fault doesnt clear
-
27-06-2012, 05:35 PM #7
Re: carrier vector 1500 high pressure 410 psi
this is not active fault
-
29-06-2012, 03:44 PM #8
Re: carrier vector 1500 high pressure 410 psi
I have a 1550 manual vector.
mcnc6@msn.com
-
29-06-2012, 03:55 PM #9
Re: carrier vector 1500 high pressure 410 psi
vector 1550.jpg
thanks
-
02-07-2012, 01:25 AM #10
Re: carrier vector 1500 high pressure 410 psi
thanks so much