    Question How to solve STT fail Error on MYCOM CPIII , VLD200



    Dear Friends
    Hi, We have a Mycom 200vld compressor and it was work well but , it just stop some times and show STT fail on CPII monitor.
    i check the manual and it said that :
    compressor running confirmation,a contact of the motor starter on digital input2 , is not detected by the CP-III/E when compressor start signal was given.

    Does anybody know how to get ride of this alarm and solve it?

    Thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: How to solve STT fail Error on MYCOM CPIII , VLD200

    Hi Jahangir.
    A good place to start would be to check your Compressor Motor Start Feedback.
    Which has a relay (MSRB) which is normally open circuit through terminals 12a and 12b on your Digital input / output board. this circuit makes on start-up.
    It could be as simple as the relay has failed?
    Worth a check anyway.
    Grizzly

    wiring diag. to follow.

    http://www.mediafire.com/?ab67syeepmc7cah

    Wiring diagram. may help?
    Last edited by Grizzly; 25-06-2012 at 06:02 PM.

  3. #3
    Join Date
    Dec 2006
    Location
    Iran
    Age
    43
    Posts
    55
    Rep Power
    18

    Re: How to solve STT fail Error on MYCOM CPIII , VLD200

    Hi Grizzly.
    you mean than , when compressor is running the 12a and terminal COM should be close? if then might be another problem or something else?

    Thanks
    \\******************

    I check the file . so thanks anyway

    Regards.