How to solve STT fail Error on MYCOM CPIII , VLD200
Dear Friends
Hi, We have a Mycom 200vld compressor and it was work well but , it just stop some times and show STT fail on CPII monitor.
i check the manual and it said that :
compressor running confirmation,a contact of the motor starter on digital input2 , is not detected by the CP-III/E when compressor start signal was given.
Does anybody know how to get ride of this alarm and solve it?
Thanks
-
25-06-2012, 05:28 PM #2
Re: How to solve STT fail Error on MYCOM CPIII , VLD200
Hi Jahangir.
A good place to start would be to check your Compressor Motor Start Feedback.
Which has a relay (MSRB) which is normally open circuit through terminals 12a and 12b on your Digital input / output board. this circuit makes on start-up.
It could be as simple as the relay has failed?
Worth a check anyway.
Grizzly
wiring diag. to follow.
http://www.mediafire.com/?ab67syeepmc7cah
Wiring diagram. may help?Last edited by Grizzly; 25-06-2012 at 06:02 PM.
-
25-06-2012, 05:39 PM #3
Re: How to solve STT fail Error on MYCOM CPIII , VLD200
Hi Grizzly.
you mean than , when compressor is running the 12a and terminal COM should be close? if then might be another problem or something else?
Thanks
\\******************
I check the file . so thanks anyway
Regards.Last edited by Jahangir; 25-06-2012 at 08:51 PM.