    Frost on suction line



    At a friends house the other day and checked on an 15kW R22 split sytem unit with capillary expansion, unit is approx 10 years old with frost on suction line right up to compressor, unit operating on heating, all fans running and some heat coming from ceiling vents, filters are clean, outdoor temp 8*C, indoor 17*C, air from ceiling vent 26*C, did not have gauges with me. Frost build up starts to occur after only operating for a few minutes operation, complaint was unit running for longer time with reduced heating, looks like unit under charged, any other reasons that could cause this frost to occur?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Frost on suction line

    Not enough air passing through the evaporator (outdoor coil)?

    .

  3. #3
    Join Date
    Feb 2007
    Location
    Australia
    Posts
    25
    Rep Power
    0

    Re: Frost on suction line

    There was no visible frost on the evaporator at the time the suction line was frosting up and although I had no air flow meter there appeared to be sufficient air movement over the coil.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Frost on suction line

    Sounds like over charged system and refrigerant boils in the suction line.

  5. #5
    Join Date
    Feb 2007
    Location
    Australia
    Posts
    25
    Rep Power
    0

    Re: Frost on suction line

    Unit has been operating for several years without any obvious problems and has not had any service work done (as advised)
    Is it possible that there is a restriction in the capillary or distributor tubes to the evaporator (outdoor) coil.
    Think I am going to have get back to the unit and take more readings.

  6. #6
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Frost on suction line

    Double check the external heat exchanger (evaporator) including the airflow of the fan and clean the battery.

  7. #7
    Join Date
    Feb 2007
    Location
    Australia
    Posts
    25
    Rep Power
    0

    Re: Frost on suction line

    Certainly will be checking airflows but what is "clean the battery".
    If relating to temps taken these were via digitemp themometer and were checked a number of times.

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Frost on suction line

    by battery might be referring to coil