    Dear All,

    Would it still be OK to replaced an existing Helical oil separator by a conventional type oil separator of the same capacity? Was there any effect in the system if this will be done?

    Appreciate your comments on the above mattter.

    Best regards,

    kaelte_technik
    Last edited by kaelte_technik; 21-06-2012 at 08:49 AM.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Helical Oil Separator replaced by a conventional oil separator

    .

    Yes. Oil seperators are oil seperators........

    Some designs work slightly better than others and some are designed
    for specific jobs but if you are working and a straight forward system I
    can't see any reason why you can't put any equal capacity oil sep onto the
    system.

    Regards

    Rob.

  3. #3
    Join Date
    Mar 2006
    Location
    Philippines
    Posts
    35
    Rep Power
    0

    Re: Helical Oil Separator replaced by a conventional oil separator

    Thanks Rob

    Basicallly the existing one (Helical and sealed type) is connected to a compressor rack (Linde) and we are replacing due to problem of clogging and we cannot find in the market the of the same model that is why we are replacing it with a conventional type.

    Regards,

    kaelte_technik

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Helical Oil Separator replaced by a conventional oil separator

    Quote Originally Posted by kaelte_technik View Post
    Thanks Rob

    Basicallly the existing one (Helical and sealed type) is connected to a compressor rack (Linde) and we are replacing due to problem of clogging and we cannot find in the market the of the same model that is why we are replacing it with a conventional type.

    Regards,

    kaelte_technik
    As long as the new oil sep is the some capacity I can't see
    any reason why you can't swap it for another type.