    superheat on residential systems



    Ok sorry if this question seems really amateur but on residential systems do you all climb into the attic or crawl space to get line temps or are they only taken at the service valves to do the calculations?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: superheat on residential systems

    measure temp at the bulb-an apprentice is good for this- then compare with your gauges on the condenser- and then ring him-as all apprentices haves mobys-make sure he knows where to stick the temperature probe

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: superheat on residential systems

    If this is an American style system i believe the correct method is to measure at the outdoor unit and compair it to the manufacturers chart, depending on model you either charge to superheat or subcooling.

    It goes without saying that filters and coils need to be clean, with proper air flow through the coil etc.

    If it was a refrigeration system though you would check at the txv bulb.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    May 2010
    Location
    ipswich
    Age
    31
    Posts
    26
    Rep Power
    0

    Re: superheat on residential systems

    (I assume you know how to measure SH and SCL) if it requires you (or an apprentice) to crawl in an attic then yes.