    R22 retrofit flooded Industrial plant



    Has anyone changed refrigerant in a flooded R22 plant with good results?

    Have a plant with approx 700kg of R22 with a flooded shell & tube heat exchanger.
    Refrigerant on tube, side single stage economized plant with screw compressor.

    -40 C sst mineral oil used.

    Have had R434A recommended, any other suggestions etc

    Thanks



  2. #2
    Join Date
    Jan 2010
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: R22 retrofit flooded Industrial plant

    First off, using a refrigerant with glide in a flooded system is not the preferred option, however R-434A has minimal glide, similar to R-404A. The pressure of R-434A is approximately 25% higher than R-22, so it will require modification of the system to account for the different properties of the refrigerant. The cost to retrofit from R-22 to R-434A may be substantial.


    If you are going to put a lot of money into the system, it may be better to go with a more mainstream refrigerant with minimal glide like R-507 or R-404A. The availability and cost should be much more attractive in the long term than with a limited availability refrigerant like R-434A.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: R22 retrofit flooded Industrial plant

    Quote Originally Posted by superslim007 View Post
    First off, using a refrigerant with glide in a flooded system is not the preferred option, however R-434A has minimal glide, similar to R-404A. The pressure of R-434A is approximately 25% higher than R-22, so it will require modification of the system to account for the different properties of the refrigerant. The cost to retrofit from R-22 to R-434A may be substantial.


    If you are going to put a lot of money into the system, it may be better to go with a more mainstream refrigerant with minimal glide like R-507 or R-404A. The availability and cost should be much more attractive in the long term than with a limited availability refrigerant like R-434A.
    At the moment everything shows for easy replacement, no oil change, no real pressure change, same capacity, similar price to R22 in Australia!

  4. #4
    Join Date
    Feb 2010
    Location
    Greece
    Age
    49
    Posts
    7
    Rep Power
    0

    Re: R22 retrofit flooded Industrial plant

    i ve replaced r 22 with r 422 that has similar characteristic with the old but you need to change the oil with polyester oil!

  5. #5
    Join Date
    Feb 2010
    Location
    Greece
    Age
    49
    Posts
    7
    Rep Power
    0

    Re: R22 retrofit flooded Industrial plant

    www2.dupont.com/Refrigerants/en_GB/products/isceon29.html