    Apr 2002
    Canada
    66
    Ammonia Refrigeration Cold storage
    An Industrial Cold storage having Ammonia refrigeration system having Frick screw compressors., how much minimum quantity(%) of ammonia liquid to be required in Therm o-siphon tank for cooling the oil of screw compressors.
    g.karsandas:
    3,360
    Re: Ammonia Refrigeration Cold storage
    g
    Is the vessel only for thermosyphon, if so
    Usually 30-50% full or 5 minutes of running at peak load for a buffer if whatever happens to keep prime of t/syphon circuit.
    Apr 2002
    Canada
    66
    Hi Ranger 1,
    From thermosyphon tank,refrigerant goes to various temperature accumulator tanks.
    And how to judge that the units are running at the maximum because of various temperature zone,and numbers of compressors are running at various load.
    Thanks,
    g.karsandas
    3,360
    Quote Originally Posted by g.karsandas View Post
    Hi Ranger 1,
    Thanks,
    g.karsandas
    You describe a combination thermosyhon & liquid reciever.
    I would still suggest minimum 30% to 40% level at all times for reliable operation.
    Sep 2008
    Canada
    811
    g.karsandas:
    Do you have any concerns?