    Ammonia Refrigeration Cold storage



    An Industrial Cold storage having Ammonia refrigeration system having Frick screw compressors., how much minimum quantity(%) of ammonia liquid to be required in Therm o-siphon tank for cooling the oil of screw compressors.
    g.karsandas:



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia Refrigeration Cold storage

    g
    Is the vessel only for thermosyphon, if so

    Usually 30-50% full or 5 minutes of running at peak load for a buffer if whatever happens to keep prime of t/syphon circuit.

  3. #3
    Join Date
    Apr 2002
    Location
    Canada
    Age
    66
    Posts
    16
    Rep Power
    0

    Re: Ammonia Refrigeration Cold storage

    Hi Ranger 1,
    From thermosyphon tank,refrigerant goes to various temperature accumulator tanks.
    And how to judge that the units are running at the maximum because of various temperature zone,and numbers of compressors are running at various load.
    Thanks,
    g.karsandas

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia Refrigeration Cold storage

    Quote Originally Posted by g.karsandas View Post
    Hi Ranger 1,
    From thermosyphon tank,refrigerant goes to various temperature accumulator tanks.
    And how to judge that the units are running at the maximum because of various temperature zone,and numbers of compressors are running at various load.
    Thanks,
    g.karsandas


    You describe a combination thermosyhon & liquid reciever.
    I would still suggest minimum 30% to 40% level at all times for reliable operation.

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Ammonia Refrigeration Cold storage

    Quote Originally Posted by g.karsandas View Post
    An Industrial Cold storage having Ammonia refrigeration system having Frick screw compressors., how much minimum quantity(%) of ammonia liquid to be required in Therm o-siphon tank for cooling the oil of screw compressors.
    g.karsandas:
    Do you have any concerns?