    total fresh air handler



    Dear sirs,
    I've a design on hand for a total fresh air handler.
    #Design paremeters as below:
    --The inlet air DB is 29degree celsius,humidity 19g/kgdryair
    --the outlet air DB 18 degree celsius,humidity is 6.8g/kgdryair
    --air volume is 650m3/h
    **The system is going to be designed as one compressor\DX coil (for dehumidifying inlet air)\evaporative condenser\reheating coil\hot gas bypass valve etc.
    **the process is inlet air --DX coil(to machine dewpoint 9.88C RH90%)--reheating coil (to 18C,humidity unchanged)--to required space
    When the inlet air enthalpy is lower than designed condition,the DX coil load is less ,so the bypass valve open and keep the evap pressure head not down.
    my concerns are:
    --if the DX coil load is reducing,bypass valve can keep the evap temp constant? if no,how to do?
    --if the compressor is constant volume type, the bypass valve can play the role to adjust compressor capacity to meet the DX load?
    --reheating coil is parellel to evaporative condenser,the heating capacity is changed while machine dewpoint is varied with the inlet air paremeters,i don't want make the control too complex,is on/off control (EM valve for the coil)reasonable?
    --how do you think what the best system for this total fresh air handler?

    welcome any comment

    best regards
    LC-


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Sep 2005
    Location
    Australia
    Age
    68
    Posts
    7
    Rep Power
    0

    Re: total fresh air handler

    use an enthalpy wheel

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: total fresh air handler

    Hi frigidfridgie
    I'm not clear how about the efficiency applying enthalpy wheel in so small volume air flow. What type system you recommend?-
    Thanks for your reply,you're the first one to answer this. May be it's not a interesting topic-

    rgds
    LC-
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: total fresh air handler

    Pitcure would help!

    Renato

Similar Threads

  1. Quick freezing of fresh products
    By maxim971 in forum Technical Speculations
    Replies: 12
    Last Post: 18-09-2009, 11:06 PM
  2. fresh air heating in cold area
    By Lc_shi in forum Air Conditioning
    Replies: 7
    Last Post: 14-05-2009, 01:37 AM
  3. split units with fresh air
    By gwilliamson in forum Domestic
    Replies: 15
    Last Post: 26-10-2005, 09:57 AM
  4. Total System Charge
    By dallan in forum Fundamentals
    Replies: 1
    Last Post: 27-12-2004, 08:18 PM
  5. Large cold room for fresh produce made of Glass
    By allanbaker in forum New Technologies
    Replies: 3
    Last Post: 11-05-2004, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •