    Daikinl4 code



    Rzp125dv 1 mfg no 3po856023a l4 code up checked the thermistor all ok dont wont to change the board on invertor dont seem to get on very well with daikin boards any possible other faults to check first? Old unit should come of the wall but need to keep it rolling ta charlie



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikinl4 code

    few things o check-
    Activation of fin thermal switch

    Faulty fin thermistor

    High outside air temperature

    Insufficient cooling of inverter radiation fin

    Blocked suction opening

    Dirty radiation fin

    Faulty outdoor inverter PC board

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikinl4 code

    Ah,
    There is another thing that Daikin don't mention in their manuals...

    We have had this happening on a few of the RZPs and what we have found working is to replace the heat transfer paste between the board and the heat sink.
    Just take the board off as if you were to replace it, clean the 2 surfaces really well getting rid of all the old paste then apply the new paste and clamp it all back together again.

    (Heat transfer paste is about £2 from places like Maplin)



    .

  4. #4
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Daikinl4 code

    thanks guys the unit does not run that long before l4 comes up and the heat sink dont even get that hot so i am presumeing its a bad board thanks for input guys

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikinl4 code

    OK,
    May I suggest that you before you order the new board reread my post above as what you are describing is the classical symptom of hardened heat transfer paste...


  6. #6
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Daikinl4 code

    ok worth a go thanks for your input will give it a go

  7. #7
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Daikinl4 code

    fitted a good board to get rid of l4 and even got the paste as suggested was going to make sure it ran ok then fit the old board it runs for about a hr and now brings up l9 code any ideas apart from the comp?

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikinl4 code

    L9
    Outdoor Unit LED
    Display
    A
    5 1 4 2 4 3 4 4 4
    Applicable
    Models
    RZP71~140D
    Method of
    Malfunction
    Detection
    Malfunction is detected by converting the current flowing to power transistor into voltage with
    CT1 (DC current sensor).
    Inverter PC board detects the disorder of position signal.
    Malfunction
    Decision
    Conditions
    When compressor overload (except for when startup) is detected
    When position signal is disordered
    Supposed
    Causes

    Faulty compressor (lock)

    Pressure differential startup

    Faulty inverter

    The stop valve is left in closed.
    looks like the compressor