    Cold storage for meat store problem



    Hi dears,

    I m Hamza from pakistan & working in a power plant as HVAC technician, some how we have a col storage of 4.0 ton capacity to maintain -18 celsius, the problem i've got that it didnot maintain TEMPRATURE TO -18 CELSIUS I HAVE CHECKED THESE ALSO can any 1 help what i do.
    :> Suction pressure is 22 psi at room temprature of -12 psi
    :> 225 psi H.P at ambient of 48 celsius
    :> Thermostate probe is away from evaporator
    :> thermostate accuracy is 98% (after testing)
    :> Thermostate was tripping compressor at temprature of -15 degree celsius
    :> expansion vallve model used in unit is danfoss TEX-5 (new installed)

    Any other steps i've checked please tell me



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45
    1. What refrigerant is used?

    2. Is the system operating and not reaching set point or is the thermostat stopping the unit before the room reached the desired temperature?

    3. What is the liquid line temperature as it comes out of the condensor? Before it enters the TEV (~6" before)?

    4. What is the suction line temperature by the TEV's bulb?


    .

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45
    Sorry,
    Also, what are the high and low side pressures when the above temperatures are taken?

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Cold storage for meat store problem

    Quote Originally Posted by The Viking View Post
    1. What refrigerant is used?

    2. Is the system operating and not reaching set point or is the thermostat stopping the unit before the room reached the desired temperature?

    3. What is the liquid line temperature as it comes out of the condensor? Before it enters the TEV (~6" before)?

    4. What is the suction line temperature by the TEV's bulb?


    .
    I presume nawaz is using R22 since he's using a TEX DANFOSS valve.

    "225 psi H.P at ambient of 48 celsius" » Something is wrong. Are you sure it is 48șC. Is the condenser air cooled or evaporative type?
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Cold storage for meat store problem

    Quote Originally Posted by Sandro Baptista View Post
    I presume nawaz is using R22 since he's using a TEX DANFOSS valve.
    OK,
    But as he looking at a freezer where he want to maintain -18șC R22 is an unlikely candidate, hence the TEV might be the wrong one... Or, it might been designed as a fridge and someone just lowered the set point.

    There are a lot of strange data in the OP, therefore "back to basics":

    1. What refrigerant is used?
    2. Is the system operating and not reaching set point or is the thermostat stopping the unit before the room reached the desired temperature?
    3. What is the liquid line temperature as it comes out of the condensor? Before it enters the TEV (~6" before)?
    4. What is the suction line temperature by the TEV's bulb?
    5. What are the high and low sides' running pressures?

    Oh, not forgetting the all important;
    6. Has this system managed to maintain -18șC in the past?



    .

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Cold storage for meat store problem

    Check the refrigeration system for refrigerant leak...a minute leak could result i temperature shift .