    chiller frick



    hy guys:

    I have a system of ammonia chiller operating as the plate heat exchanger is flooded with ammonia. my question is: because at a low suction pressure (30psig) if the water temperature is 9 ° c? thanks



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: chiller frick

    At 30psig, evaporating around -9.0 'c , split too big, suggest checking water flow rates too high, alternatively evap HX is not fully flooded. Suction strainer partially blocked.
    More system information would help.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: chiller frick

    Hi Magoo.
    If I am correct, the system serviceman may be referring to is similar to the Sabroe packs.
    If that is indeed the case, then I would be checking as you say the flow rate of the water through the PHE.

    Also the charge level as they tend to struggle if the level is not suffice.
    This is, as I suggest. Dependant upon what Serviceman is dealing with.
    Grizzly

  4. #4
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: chiller frick

    You should try to drain the oil from your PHE. probably something wrong with your oil return

  5. #5
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: chiller frick

    I'll upload some pictures of the system in a while to see what I can support. thanks

  6. #6
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: chiller frick

    Ammonia is a system that cools water, we have 03 compressors RXF-39 with 125hp engine, use water to cool edible soybean oil, water must go back to 8 ° C and 12 °. thanks

  7. #7
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: chiller frick

    this day so the machine was operating ps = 49psig ts = 5.3 ° c tchw = 9.2 ° c dp = 161 psig dt = 58.2 ° c % = 47.1% compressor 717 refrigerant