    Air-con Compressor Burnt Due To Wrong Wiring On Capacitor



    Hi all;

    I need some consult on the compressor burn due to the wrong wiring on the capacitor for air-con. I also attached some comment i get from another source, i need just to confirm is it true on the comment?


    Wrong wiring.JPG



  2. #2
    Join Date
    Jan 2012
    Location
    malaysia
    Posts
    12
    Rep Power
    0

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Here i also attached the wire diagram also, i think is wrong wiring on the compressor. Where the life and neutral is connected at one side of capacitor and neutral at the another side.WD.JPG

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Hi Huntersouls
    In the first picture left is ok, right is wrong. Start Cap should be wired in series & Run Cap should be wired parallell with respect to phase & neutral.
    As for the second picture it looks ok to me but...

  4. #4
    Join Date
    Jan 2012
    Location
    malaysia
    Posts
    12
    Rep Power
    0

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Quote Originally Posted by Tesla View Post
    Hi Huntersouls
    In the first picture left is ok, right is wrong. Start Cap should be wired in series & Run Cap should be wired parallell with respect to phase & neutral.
    As for the second picture it looks ok to me but...
    Thank for the reply but my main question is start would it cause the fan run in reverse direction? cand cause the compressor burn.Thank you

  5. #5
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Problem is your second picture does not indicate which is start or run winding - there are so many different configurations, if you could check an old kirby service book or other you will see. I have come accross a few wireing diagrams on motors in the past few years that do not show indside winding configuration (start/common/run other) which leads to confusion in wireing externally.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    As Tesla said, left top is right.
    It can happens to the most experienced engineer. It have nothing to do with the direction of rotation of the fan, that's another story.

  7. #7
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Fans may run in the reverse direction when the cap is connected to the run (wrong) winding, but, not for very long : the start winding is wound of a thinner wire that would overheat and burn.

    Probably, some compressors may too.
    Last edited by Yuri B.; 07-06-2012 at 07:48 PM.

  8. #8
    Join Date
    Sep 2008
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    the second picture is right...the capacitor neutral terminal are connected to each other based on the design of the capacitor itself, while the live terminal is on the other side.

  9. #9
    Join Date
    Jun 2012
    Location
    sydney
    Age
    49
    Posts
    1
    Rep Power
    0

    Re: Air-con Compressor Burnt Due To Wrong Wiring On Capacitor

    Capacitor are mostly used to store energy and the release energy. without capacitor you do not imagine any circuit.
    Last edited by frank; 19-06-2012 at 09:00 PM.