    Roll Up Rapid Door gets sucked on defrost end



    Hello my friends.
    I'm having this odd problem, we installed a big freezer (3,600m3) at -20°C whit one rapid roll up door (2.50mx4.80m) that is getting "sucked" into the room when electric defrost ends. I have installed two pressure relief valves with a capacity of 7,300lts/min (calculated on formula Q=k*dT*vol).

    I have no clue on what is creating this effect, please advice.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Roll Up Rapid Door gets sucked on defrost end

    Possible that the coil chill time period before fans restart is too long and creating a rapid air density change when fans do start. Alternatively if you have multiple evaporators, stagger the defrosts, not all at once
    I had the problem of blowing rapid doors out, never really had them sucking in.

  3. #3
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Roll Up Rapid Door gets sucked on defrost end

    I'll try setting up less chill time to see how it works.

  4. #4
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    19

    Re: Roll Up Rapid Door gets sucked on defrost end

    Quote Originally Posted by georgedvf View Post
    Hello my friends.
    I'm having this odd problem, we installed a big freezer (3,600m3) at -20°C whit one rapid roll up door (2.50mx4.80m) that is getting "sucked" into the room when electric defrost ends. I have installed two pressure relief valves with a capacity of 7,300lts/min (calculated on formula Q=k*dT*vol).

    I have no clue on what is creating this effect, please advice.
    dear friend,

    u got excellent sealing of doors , this problem is because pressure inside unit reduced due to low temp, I faced similar problem we solved it by putting one way valve into the cabinet,

    regds.

  5. #5
    Join Date
    Jul 2007
    Location
    Iraq
    Posts
    43
    Rep Power
    0

    Re: Roll Up Rapid Door gets sucked on defrost end

    please reduce maximum defrost time and maximum temp for defrost ending

  6. #6
    lhill's Avatar
    lhill Guest

    Re: Roll Up Rapid Door gets sucked on defrost end

    you need to install more "equalizing valves" or make shure the ones you have are working

  7. #7
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Roll Up Rapid Door gets sucked on defrost end

    We also faced similar problems. We placed pressure equalizer valve just above this roll up door & till date this issue has never been noticed again.

  8. #8
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Roll Up Rapid Door gets sucked on defrost end

    We already had two equalizer valves working above the door and still had the problem.

    What we did was programing auto open events on the PLC, so those auto-opens works for releasing pressure.

    Thank you all.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Roll Up Rapid Door gets sucked on defrost end

    Still cannot understand why the room pressure drops and sucks in the flexible doors. OK I have had rooms over pressurizing and blowing doors out and sliders being blow off runners.
    Possibly the condensate draining is so high and pipe is too small and velocity is high and dragging air from room/enclosure even with a P trap in drain. A bit like taking plug out of a bath full of water. Velocity sucks air.

    magoo