Results 1 to 10 of 10
  1. #1
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Condensers heat reject capacity regulation



    Hi Guys,

    I'd like to hear from you guys how do you manage the heat reject capacity when you have several parallel compressors working on the same plant.

    I think the best is whenever is possible all of them remaining working with the ventilation at same speed with a frequency converter (from reduced rpm until the 100% rpm) as the mechanical power consumption depends on N^3 (rpm^3).
    The same reasoning applies to the Dahlander motors insteaad of the inverters.

    Thanks


    To make progress is never good enough, I want to do better and better and better

  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Condensers heat reject capacity regulation

    Any comments?
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Condensers heat reject capacity regulation

    sTILL Any comments?
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condensers heat reject capacity regulation

    to my opinion, this is the best solution.
    http://www.ebmpapst.com/en/products/...axial_fans.php

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensers heat reject capacity regulation

    I missed this post. Did you mentioned about air condensers or evaporative condensers? This is right for air condensers.

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Condensers heat reject capacity regulation

    Quote Originally Posted by Sandro Baptista View Post
    Hi Guys,

    I'd like to hear from you guys how do you manage the heat reject capacity when you have several parallel compressors working on the same plant.

    I think the best is whenever is possible all of them remaining working with the ventilation at same speed with a frequency converter (from reduced rpm until the 100% rpm) as the mechanical power consumption depends on N^3 (rpm^3).
    The same reasoning applies to the Dahlander motors insteaad of the inverters.

    Thanks
    Sorry, I meant ...several condensers working in parallel.

    I was thinking about evaporative condenser but I think the same principle (ventilation operating scheme) can be applied to air condensers.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Condensers heat reject capacity regulation

    Quote Originally Posted by chemi-cool View Post
    to my opinion, this is the best solution.
    http://www.ebmpapst.com/en/products/...axial_fans.php
    Sorry Chemi, I can't see the relevance with my first post.
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensers heat reject capacity regulation

    Reducing fan speed from 100% to 90% saves 27% of fan energy. From 50% to 40%, he same 10% speed reduction, save just 6% of fan energy. Sometimes it is more efficient to switch off water pumps.

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Condensers heat reject capacity regulation

    I think is better from efficient point of view switch off the fans. Also turning on and off the water pumps could lead for the formation of scale on the coil.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensers heat reject capacity regulation

    It is up to you. However, to run pumps without fans is almost useless. In North America, during cold weather many refrigeration plants cycle water pumps, because they don't have a choice. During summer operation they run pumps first. Majority of them don't have issue with the scale. To get scale you need thousands cycles of wet and dry. I know one plant that cycle pumps all year around. Yes, they have scale.