Condensers heat reject capacity regulation
Hi Guys,
I'd like to hear from you guys how do you manage the heat reject capacity when you have several parallel compressors working on the same plant.
I think the best is whenever is possible all of them remaining working with the ventilation at same speed with a frequency converter (from reduced rpm until the 100% rpm) as the mechanical power consumption depends on N^3 (rpm^3).
The same reasoning applies to the Dahlander motors insteaad of the inverters.
Thanks
To make progress is never good enough, I want to do better and better and better
-
02-06-2012, 01:32 AM #2
Re: Condensers heat reject capacity regulation
Any comments?
To make progress is never good enough, I want to do better and better and better
-
25-06-2012, 03:52 PM #3
Re: Condensers heat reject capacity regulation
sTILL Any comments?
To make progress is never good enough, I want to do better and better and better
-
25-06-2012, 04:06 PM #4
Re: Condensers heat reject capacity regulation
to my opinion, this is the best solution.
http://www.ebmpapst.com/en/products/...axial_fans.php
-
25-06-2012, 05:26 PM #5
Re: Condensers heat reject capacity regulation
I missed this post. Did you mentioned about air condensers or evaporative condensers? This is right for air condensers.
-
26-06-2012, 08:48 AM #6
Re: Condensers heat reject capacity regulation
To make progress is never good enough, I want to do better and better and better
-
26-06-2012, 08:49 AM #7
-
26-06-2012, 03:14 PM #8
Re: Condensers heat reject capacity regulation
Reducing fan speed from 100% to 90% saves 27% of fan energy. From 50% to 40%, he same 10% speed reduction, save just 6% of fan energy. Sometimes it is more efficient to switch off water pumps.
-
27-06-2012, 09:31 AM #9
Re: Condensers heat reject capacity regulation
I think is better from efficient point of view switch off the fans. Also turning on and off the water pumps could lead for the formation of scale on the coil.
To make progress is never good enough, I want to do better and better and better
-
27-06-2012, 03:10 PM #10
Re: Condensers heat reject capacity regulation
It is up to you. However, to run pumps without fans is almost useless. In North America, during cold weather many refrigeration plants cycle water pumps, because they don't have a choice. During summer operation they run pumps first. Majority of them don't have issue with the scale. To get scale you need thousands cycles of wet and dry. I know one plant that cycle pumps all year around. Yes, they have scale.