    Unisab logic



    Hi Guys!


    first of all i am not a refrigeration engineer but a programmer, therefore please understand that my question MIGHT seem basic for you. secondly my english is not the best..

    here is my problem: i need to understand based on what logic the unisab controls the inverter and the slide. my understanding tells me that since the COP of the inverter is better than that of the slide, the control SHOULD first turn down the inverter, once the inverter is at the minimum it should regulate down the slide. so first reduce the RPM and then the slide. but this is just my understanding.. i have seen some data where the rpm was at max and the slide at 90/92%..

    why?

    shouldnt the slide be at 100% and the RPM at 90/92%? the COP would be higher in that case...

    thank you

    best regards

    Frigo



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Unisab logic

    Frigo,
    A screw is most efficient at 100% load, so as you have described is correct.

    Most screws are minimum 1440 rpm.

  3. #3
    Join Date
    Jun 2012
    Location
    italy
    Posts
    6
    Rep Power
    0

    Re: Unisab logic

    Hi ranger!

    thanks for your answer,

    but why is then the unisap controlling the RPM at max and the slide at 90% and not inversed?
    what logic makes and explains this decision?

    thanks

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Unisab logic

    frigo,
    Is this compressor an auto or manual Vi?
    Frick, Sabroe?

  5. #5
    Join Date
    Jun 2012
    Location
    italy
    Posts
    6
    Rep Power
    0

    Re: Unisab logic

    auto sabroe

  6. #6
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Unisab logic

    What was Vi at that time?
    Assume that minimum Vi for this compressor is 2.2. When suction pressure is high and discharge pressure is low, optimum Vi can be lower than 2.2. Assume that optimum Vi for current operating conditions is 1.8. So compressor over compress the refrigerant when it is loaded to 100%. Slightly unloading compressor will reduce internal Vi to 1.8 and efficiency will improve(hopefully). However, this is just my logic.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Unisab logic

    Hi, frigofer

    Quote Originally Posted by frigofer View Post
    auto sabroe
    roatatune with auto Vi? .... SAB128/163 ?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Unisab logic

    Hi Josip.

    The 163 comps we look after are fixed vi on account they are variable speed.


    Grizzly

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Unisab logic

    Josep,

    The rotatune doesn't has slide valve.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Unisab logic

    Quote Originally Posted by Segei View Post
    What was Vi at that time?
    Assume that minimum Vi for this compressor is 2.2. When suction pressure is high and discharge pressure is low, optimum Vi can be lower than 2.2. Assume that optimum Vi for current operating conditions is 1.8. So compressor over compress the refrigerant when it is loaded to 100%. Slightly unloading compressor will reduce internal Vi to 1.8 and efficiency will improve(hopefully). However, this is just my logic.
    Why do you say the Vi decrease if the slide valve go forward (as approaching to the discharge port)?

    Maybe what frigofer says it happen it may because the compressor motor is a little overload and the UNISAB decrease capacity by the slide valve. Decrease the rpms it not an option because the shaft torque absorbed by the compressor remains the same...if the condensing pressure and suction pressure remain the same.
    To make progress is never good enough, I want to do better and better and better

  11. #11
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Unisab logic

    Quote Originally Posted by Sandro Baptista View Post
    Why do you say the Vi decrease if the slide valve go forward (as approaching to the discharge port)?

    Maybe what frigofer says it happen it may because the compressor motor is a little overload and the UNISAB decrease capacity by the slide valve. Decrease the rpms it not an option because the shaft torque absorbed by the compressor remains the same...if the condensing pressure and suction pressure remain the same.
    Major reason of poor part load operation of screw compressors is when they unload internal Vi don't march external (system) Vi or pressure ratio. Compression will initiate at later stage and under compression is happen.

  12. #12
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Unisab logic

    I thought it was the opposite...I mean as the slide valve go forward also the Vi increases and the final effect was over compression, despite the fact the compression initiate later with part load.
    Last edited by Sandro Baptista; 02-06-2012 at 01:30 AM.
    To make progress is never good enough, I want to do better and better and better

  13. #13
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Unisab logic

    frigo,
    Maybe potentiometer is not calibrated properly & 92% is 100% load.
    Try to force load solenoiod & see if it loads any more, if no movement 100% load in real terms.

    With variable auto Vi slide valve travel is changed each time secondary slide valve adjusts to suit conditions.
    I would have thought slide valve would be calibrated at 100% load at maximum Vi 5 or 5.8 whatever it is.
    Then as Vi adjusts below that, main slide cannot travel as much.

    Does slide valve still pulse to load at the condition you describe?

    I have a Unisab manual but not handy right now so will check.
    Last edited by RANGER1; 01-06-2012 at 10:15 PM.

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Unisab logic

    Hi, Grizzly

    Quote Originally Posted by Grizzly View Post
    Hi Josip.

    The 163 comps we look after are fixed vi on account they are variable speed.


    Grizzly
    Yes, I know that (Vi is manually fixed according to system pressures), but OP said it is ''auto sabroe" what confused me and I was thinking there is some special rotatune execution with auto Vi !?! ... this one is not original rotatune 128/163 .... seems he has some other SAB-Frick type with inverter .... where we can have auto Vi (changing in steps) and slide for capacity control plus inverter to change rpms, but that is not original rotatune ....

    ... not sure if I guess right? must wait for OP for answer ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  15. #15
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Unisab logic

    Hi, Sandro

    Quote Originally Posted by Sandro Baptista View Post
    Josep,

    The rotatune doesn't has slide valve.
    Thanks, I know that, but valid only for original rotatune SAB 128/163 .... and not for some other SAB compressors with inverter, with auto Vi and slide, agree


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Unisab logic

    Hey Josip.
    Sorry for questioning you, I missed your question mark when i read your post first time around.

    You were obviously thinking the same as me that the rota-tune models that were being questioned.
    Don't have auto vi as many others have also said.
    Basically frigofer after only 4 posts wants to be told how to write software to control the bespoke Sabroe software.

    frigofer, if someone is willing to go into that sort of detail good luck.
    Basically the control options are 4 to 20ma or control on suction pressure.
    Obviously there are lots of other parameters to consider, which if set wrong could be a very expensive experiment.
    Who would hold the warranty, not Sabroe for sure!
    Grizzly

  17. #17
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Unisab logic

    Hi, Grizzly

    Quote Originally Posted by Grizzly View Post
    Hey Josip.
    Sorry for questioning you, I missed your question mark when i read your post first time around.

    You were obviously thinking the same as me that the rota-tune models that were being questioned.
    Don't have auto vi as many others have also said.
    Basically frigofer after only 4 posts wants to be told how to write software to control the bespoke Sabroe software.

    frigofer, if someone is willing to go into that sort of detail good luck.
    Basically the control options are 4 to 20ma or control on suction pressure.
    Obviously there are lots of other parameters to consider, which if set wrong could be a very expensive experiment.
    Who would hold the warranty, not Sabroe for sure!
    Grizzly
    not problem at all, anyone can make mistake in this or another way ... this is multinational and multilingual (back home) forum and sometimes it is easy to lost something in translation or during reading, thus easy to make a kind of mistake ... and I agree to warn me in that case, won't harm me because, for a long time I knew my limits ...


    Funny, .... reading the first post again, OP there mentioned only inverter and that was indication, unit in question is not rotatune, but I saw that toooo late , anyhow, we must wait for OP to find out what unit is in question ...

    Personally, I believe setup of Unisab III is not correct ... it is very powerful control system and uncompleted setup is coming back with undesirable response/s ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  18. #18
    Join Date
    Jun 2012
    Location
    italy
    Posts
    6
    Rep Power
    0

    Re: Unisab logic

    Hi guys!

    first of all thanks for all your answers. let me explain a little bit better what i am trying to do and what is going on here:

    as stated in the first post, my knowledge of refrigeration is approximately 1%.. i know just the basics, carnot, dew point, condensation, evaporation, molier chart and few other things. i know veeeery basically how a compressor logic works. what i have to do is write a program that does not have to be 100% accurate, it just has to be an approximation. we want to simulate a system running with and without inverters. to compare COP's and show them to the customer. if the calculation startup logic is off it does not matter too much since the simulation will be off for both cases, with and without inverter. since i am not fisically near any machine, what i didwas connect remotely to a system and downloaded the data. on this system (SAB 193 S with UNISAB III) the slide is allways below 92% except 2 situations where it goes to 97%. and ita lso goes all the way down to -1.2%. so i guess that the measurement system is some % off sclae. but since it went up to 97% some times there must be something else slightly off.

    what is important for me now is to understand why the slide is so low, because based on that i know how to code my program and what to tell others for fixing it. since i am not from this sector i have no idea if this slide "problem" is indeed a problem or if it is "normal"..

    hope that this clearified a bit the situation..

    thank you very much!

  19. #19
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Unisab logic

    frogfer,
    The Unisab starts compressor & is fully unloaded, also Vi is in lowest ratio or minimum condition.
    The Vi slide stays at minimum until slide is 100% loaded, then it can adjust to the optimal Vi ratio automatically.
    At this point both Vi & slide valve move together to optimal Vi ratio.
    Unless calibration is out or a forced unload for whatever reason, I would suggest that at 97%the Vi is close to minimum setting which is calculated by pressure difference across compressor.
    This can still mean compressor is 100% loaded, but Vi/slide valve is at a different position.

    To be sure Vi & slide valve could be recalibrated.

  20. #20
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Unisab logic

    Quote Originally Posted by Sandro Baptista View Post
    I thought it was the opposite...I mean as the slide valve go forward also the Vi increases and the final effect was over compression, despite the fact the compression initiate later with part load.
    This is simplified example. 100% loaded compressor will compress ammonia from 0 bar to 10 bar. Condensing pressure is 10 bar. No part load losses. 90% loaded from 0 bar to 9 bar. Under compression is 1 bar. 70% loaded from 0 bar to 7 bar. Under compression is 3 bar and losses will increase. And so on...

  21. #21
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Unisab logic

    Hi, frigofer

    Quote Originally Posted by frigofer View Post
    Hi guys!

    first of all thanks for all your answers. let me explain a little bit better what i am trying to do and what is going on here:

    as stated in the first post, my knowledge of refrigeration is approximately 1%.. i know just the basics, carnot, dew point, condensation, evaporation, molier chart and few other things. i know veeeery basically how a compressor logic works. what i have to do is write a program that does not have to be 100% accurate, it just has to be an approximation. we want to simulate a system running with and without inverters. to compare COP's and show them to the customer. if the calculation startup logic is off it does not matter too much since the simulation will be off for both cases, with and without inverter. since i am not fisically near any machine, what i didwas connect remotely to a system and downloaded the data. on this system (SAB 193 S with UNISAB III) the slide is allways below 92% except 2 situations where it goes to 97%. and ita lso goes all the way down to -1.2%. so i guess that the measurement system is some % off sclae. but since it went up to 97% some times there must be something else slightly off.

    what is important for me now is to understand why the slide is so low, because based on that i know how to code my program and what to tell others for fixing it. since i am not from this sector i have no idea if this slide "problem" is indeed a problem or if it is "normal"..

    hope that this clearified a bit the situation..

    thank you very much!
    You can setup your UNISAB III to measure COP, then you can setup your compressor to run constantly at some speed/frequency (3000rpm) and then play with the slide i.e. part load ... not sure in complete procedure .... never did it, only normal start up and parameters tune ... but maybe you can contact people from Sabroe how to proceed in your case ... I believe it is possible to use UNISAB III to show COP in both cases and I think that is the best way .... but I can be wrong either

    for your above problem (in bold) I think they need to adjust capacity slide and Vi slide (agree with RANGER1) or maybe compressor is working with active limiters and not allowed to reach 100% capacity... motor current, suction ramp, separator velocity etc....



    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  22. #22
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Unisab logic

    Quote Originally Posted by Segei View Post
    This is simplified example. 100% loaded compressor will compress ammonia from 0 bar to 10 bar. Condensing pressure is 10 bar. No part load losses. 90% loaded from 0 bar to 9 bar. Under compression is 1 bar. 70% loaded from 0 bar to 7 bar. Under compression is 3 bar and losses will increase. And so on...
    Segei,

    I don't see it exactly as you said. Notice that at the part load the slide valve also approach the discharge port and so the final compressor gas volume also is smaller.
    To make progress is never good enough, I want to do better and better and better

  23. #23
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Unisab logic

    Quote Originally Posted by Sandro Baptista View Post
    Segei,

    I don't see it exactly as you said. Notice that at the part load the slide valve also approach the discharge port and so the final compressor gas volume also is smaller.
    You are right when we talk about increasing Vi. However, at certain point discharge volume will achieve minimum and we have maximum Vi. After that no reduction of volume on discharge side and unloading will lead to under compression.