    3,357
    Cleanup procedure after semi hermetic screw burn out
    After some opinions on Hanbell screw semi hermetic screw, burnt out windings on a water chiller.
    What are correct procedures to clean it & system up?
    Apr 2007
    36
    371
    23
    Re: Cleanup procedure after semi hermetic screw burn out
    Remove old compressor test for acidity of oil**
    Flush system pipework, coils etc
    New drier
    Fit burn out drier
    Add acid treatment to new compressor**..........if you use it
    Vac and charge system as per normal practice
    Return to site after running for a while and test p/drop across burn out drier and follow instructions provided with drier for changing etc
    j
    3,357
    Could you change the total refigerant charge, vac out & not install suction burn out filters, only liquid line filter/driers?Also change oil of course.
    Apr 2007
    36
    371
    23
    I would be reclaiming the whole charge and the new comp will have new oil anyway. You don't have to install burn out driers its entirely up to you. I personally think its job dependant and dependant on acid level and what the customer will pay for. Burn out driers are pricey and a pain to change if reqd if they are brazed in.
    Aug 2007
    Sydney
    1,083
    23
    Hi Ranger keep checking oil acid levels at intervals with TKO acid test kits & change oil until no acid is indicated. Then do an oil analysis lab test to confirm/prove successful clean up. As well as all above of course.
    Almost forgot - remove suction line filters (if used) after a month of clean running, they have a tendancy to block up over time & reduce efficiency.
    Auckland
    74
    3,357
    37
    Hi Ranger1,
    were you able to establish the cause of initial failure.
    3,357
    Thanks for replies, burn out may have been due to faulty starter gear.
    I had never heaed of replacing whole charge before, just thought install suction burn out filters.
    Obviously oil change & monitor.
    The Hanbell also has built in oil seperator, so thought it might need taking off & cleaning, but this did not happen, just oil change for compressor, refrigerant charge change & evacuation.