Results 1 to 8 of 8
  1. #1
    Join Date
    Dec 2006
    Location
    Indonesia
    Age
    74
    Posts
    37
    Rep Power
    0

    is this possible - URGENT



    Hi,
    I have a 5 HP rotary compressor and I'd like to bring 3000 liter of water (for a spa) from 30 degree C down to 5 degree C.
    Is it possible to do so with 5 HP compressor, and if it is, roughly how long will it take? Thanks!



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Posts
    235
    Rep Power
    20

    Re: is this possible - URGENT

    Is this compressor part of chiller?
    Are you considering building a chiller?
    Is the water in a storage container or do you need to chill it whilst flowing?
    Let us have some more information
    Location, United Kingdom

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    59
    Posts
    243
    Rep Power
    16

    Re: is this possible - URGENT

    Quote Originally Posted by ysh1317 View Post
    Hi,
    I have a 5 HP rotary compressor and I'd like to bring 3000 liter of water (for a spa) from 30 degree C down to 5 degree C.
    Is it possible to do so with 5 HP compressor, and if it is, roughly how long will it take? Thanks!
    Short answer is yes...

    But (and it is a BIG but) how long do you want it to take to pull the temperature of the water down.

    You are dealing with 3000 kg of water reduced by 25 degK and that will require
    a long time to complete the process.

    coolrunnings

  4. #4
    Join Date
    Dec 2006
    Location
    Indonesia
    Age
    74
    Posts
    37
    Rep Power
    0

    Re: is this possible - URGENT

    The 5HP (+/- 45.000 BTU) is a part of a chiller unit, the water will be contained in a concrete space (for a spa).
    So the water from the spa will be pumped into the chiller/cooling coil, then circulated back into the spa.

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Posts
    235
    Rep Power
    20

    Re: is this possible - URGENT

    Is the storage tank insulated or is this "concrete space" part of the spa?
    If as you state the water is at 30C does this reflect the fact that the surrounding space is at a similar temperature?
    What is the water to be used for in the spa, is it a cold plunge pool?
    Location, United Kingdom

  6. #6
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: is this possible - URGENT

    To decrease 1 liter of water to a degree required 1 Kcal in 1 hour, then to decrease 3000 liters of 25 degrees needed 75,000 fr / h (64.5 KW), a compressor 5hp with R407C makes about 12,500 fr /, making the calculation with this potential will take about 6 hours, so if the water is completely isolated from external heat sources.

  7. #7
    Join Date
    Dec 2006
    Location
    Indonesia
    Age
    74
    Posts
    37
    Rep Power
    0

    Re: is this possible - URGENT

    Quote Originally Posted by B G Scott View Post
    Is the storage tank insulated or is this "concrete space" part of the spa?
    If as you state the water is at 30C does this reflect the fact that the surrounding space is at a similar temperature?
    What is the water to be used for in the spa, is it a cold plunge pool?
    Sorry I should've been more clearer (pardon my English)...
    This is for a cold spa, so the water itself will be in the spa tube made of concrete with ceramic tiles.
    The spa itself will be in an enclosed room, separated from the hot water spa.
    The surrounding area should be around 30°C most of the time because of the tropical climate down here (Indonesia).

  8. #8
    Join Date
    Dec 2006
    Location
    Indonesia
    Age
    74
    Posts
    37
    Rep Power
    0

    Re: is this possible - URGENT

    Quote Originally Posted by mark957 View Post
    To decrease 1 liter of water to a degree required 1 Kcal in 1 hour, then to decrease 3000 liters of 25 degrees needed 75,000 fr / h (64.5 KW), a compressor 5hp with R407C makes about 12,500 fr /, making the calculation with this potential will take about 6 hours, so if the water is completely isolated from external heat sources.
    Thank you mark957 for the answer, certainly helps!