    Question troubleshoot a two door storage room



    Hi all.We have a two door storage room with a static evaporator, capillary feeding type, in the middle distance between the dryer and the room the capillary is cold (it’s supposed to be little warm), an ice collected on the capillary tube when the tube enters the room and a big block of ice formed on the first 10 cm of the evaporator And the rest of evaporator is not cold enough to drop down the temperature of the room The low pressure is 2 bar (R22). What could be the problem? Lack of feeding clogged capillary tube or filter.The system maybe modified (it's an old storage room).



  2. #2
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: troubleshoot a two door storage room

    Unit does not have enough refrigerant.
    Probably a bad evaporator


    Good luck

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: troubleshoot a two door storage room

    an ice collected on the capillary tube when the tube enters the room and a big block of ice formed on the first 10 cm of the evaporator
    could be looking at a restriction or shortage, without looking up press/temp comparasons for R22, I would say that the gas charge should be looked at.

    And the rest of evaporator is not cold enough to drop down the temperature of the room
    Sounds like the evap is not full of liquid - another sure sign to check the charge.

    The low pressure is 2 bar (R22).
    What temp are you trying to evaporate at?
    Do you have any readings for the high side?

  4. #4
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Exclamation Re: troubleshoot a two door storage room

    Try to measure the difference in temperature (mesure pipe line 10 cm before filter dryer and 10 cm after filter) If the temperature diference is biger then 1 K then replace the filter.The evaporating temperature reading on the gauge should be 14 K lover the desire temperature in the room.

    good luck

  5. #5
    Join Date
    Oct 2005
    Location
    kent , england
    Posts
    27
    Rep Power
    0

    Re: troubleshoot a two door storage room

    sounds like gas charge low if cap blocked would expect low side in a vacume but check high side someone may of overcharged system thinking gas charge low because of a blockage , most likely sog though
    chill out it's only a fridge

  6. #6
    william_wye's Avatar
    william_wye Guest

    Re: troubleshoot a two door storage room

    What temp are you trying to achive and what is your head press? Pump down unit to test efficincy

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: troubleshoot a two door storage room

    William, I think that you are a little late in thoughts on this one, check the date of the previous post
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: troubleshoot a two door storage room

    Always nice/polite if you come back once here - even if it's weeks later - and tell us what you've found.
    We've taken the efforts to answer your questions, to give possible solutions, so the least we can expect is some feedback.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Cheese Room Design 24V DC
    By jbelding in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2006, 03:23 PM
  2. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM
  3. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM
  4. Non Defrosting Room
    By David PS in forum Technical Discussions
    Replies: 9
    Last Post: 02-01-2004, 01:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •