Results 1 to 15 of 15
    Apr 2012
    Iraq
    30
    614
    11
    charging problem
    i have craft type 2 ton ac window type
    during charging i encounter a problem
    condenser is separated into 2 separated heat zone
    one cold and one hot
    so why that is happen
    Power consists not in being able to strike another but in being able to control oneself when anger arises
    Apr 2007
    30
    372
    Re: charging problem
    Let me clarify...your condenser is half hot and half cold?
    Oct 2008
    mallorca, spain,
    69
    771
    13
    why is this < http// you tube on a website for a/c units ? < = sedgy
    lebanon
    130
    11
    hi
    there is a restriction there is a small filter at the bottom of the condenser check it
    Apr 2012
    Iraq
    30
    614
    11
    thank you for your reply
    Apr 2012
    Iraq
    30
    614
    11
    Quote Originally Posted by jdunc2301 View Post
    yes that is what i am meaning
    Oct 2008
    newbury
    57
    1,379
    29
    Quote Originally Posted by kefah View Post
    did you weigh the charge in?
    Apr 2012
    Iraq
    30
    614
    11
    Quote Originally Posted by r.bartlett View Post
    yes i weght it
    Apr 2007
    30
    372
    Restriction then
    Jul 2010
    NTH.QLD Australia
    56
    1,757
    27
    You using the right type of refrigerant? What is the suction pressure?
    Apr 2012
    Iraq
    30
    614
    11
    can you explain more
    Apr 2012
    Iraq
    30
    614
    11
    Restriction then
    Apr 2012
    Iraq
    30
    614
    11
    Quote Originally Posted by mikeref View Post
    yes its right type of refrigerant
    Apr 2007
    30
    372
    Restriction would mean theres a blockage restricting the flow of refrigerant....if there is a restriction it could technically work like an expansion device as one side of the restriction will be high pressure and the other side of the restriction would be a lower pressure.......thats the best way i can explain what i mean its too early in the morning to get my brain working!
    Apr 2012
    Iraq
    30
    614
    11
    thank you every one for helping me