    Air Dryer problem - Boge

    Can somebody please advise me on the following problem.

    Equipment - BOGE Refrigerant air dryer, model D670, type-429,
    R134a, 17kg, LP/HP op. pr are -16/20bar.

    The above dryer was tripping on LP earlier. then on doubt replaced the filter drier and cleaned the expansion valve and put back. gas charged but the problem is not solved. amount of gas charged from lp side is about 15kg (not allowing further due to the tripping on LP). we tried by heating the gas cylinder also.

    observations-
    when compressor is in running, HP side reading is 19bar, LP is gradually coming down to 2bar.
    There is ice formation on expansion valve & up to evaporator inlet.
    no icing on evaporator & temp is around 40deg.
    no cooling on evaporator to accumulator piping

    is there any chance of complete choking of evaporator?

    there is also a bypass tubing (flo-con installed) from HP to vapor line.

    Please advise what to do.

    regards
    tvrao

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Air Dryer problem - Boge

    You say there is ice forming after the TXV, I would check that it hasn't lost the charge, orifice can also be a problem, replace it and try again, its the cheapest part of the system.

  3. #3
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Air Dryer problem - Boge

    Looks like a restriction at the exp valve. Just an idea try taking the bulb out and putting it in hot water to see if that will open the valve , keeping an eye on the lp whilst doing so.