    R422d



    We have recently changed from R22 to R422D but now the compressors are running continuously any ideas on what to next

    Regards

    Dave



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: R422d

    Yeah give us more info :-)
    plant type ,application etc.etc
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Jun 2010
    Location
    Wales
    Posts
    45
    Rep Power
    0

    Re: R422d

    Hope you changed every gasket/ seal on the system aswell
    otherwise say goodbye to all the charge!


    Luke

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R422d

    Quote Originally Posted by Allen Key View Post
    We have recently changed from R22 to R422D but now the compressors are running continuously any ideas on what to next

    Regards

    Dave
    Put the R22 back in, you lose upto 30% capacity with R422D.

    Or change the oil to poe and run it on R407F, have a word with A-Gas.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: R422d

    Yes, that's right. Now you have less capacity so the compressors have to work longer so the heat load energy from the refrigerated spaces can be dissipated...and probably on the summer the plant sometimes even can't reach the desired temperature.
    But if the evaporator temperature is lower than the usual it may indicate that the evaporators and suction filters are dirt with oil waste.
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: R422d

    Quote Originally Posted by Luke.G View Post
    Hope you changed every gasket/ seal on the system aswell
    otherwise say goodbye to all the charge!


    Luke
    It is a drop in refrigerant...if you didn't changed the oil you don't need to change the elastomeric seals.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: R422d

    its the same old story like when they got rid of r12/r502 the drop ins were a nightmare condensor pipes turning blue etc!but hey we have had long enough to scrap this old plant!

  8. #8
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: R422d

    Quote Originally Posted by Sandro Baptista View Post
    It is a drop in refrigerant...if you didn't changed the oil you don't need to change the elastomeric seals.
    Hi Sandro,

    The "drop ins" were those which replaced R12 some years ago. Those refrigerants did not have big miscibility/sollubility problems with MO, as they were HCFC's.

    The problem now, is that the new substitute gases, such as R422D are mostly HFC's blends(around 97%), so, an oil change should be recommended. Otherwise, there will be oil return problems. Sometimes these problems arise in a few minutes, some other they show up in 1 year.

    Regards,

    Nando.

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: R422d

    Quote Originally Posted by Fri3Oil System View Post
    Hi Sandro,

    The "drop ins" were those which replaced R12 some years ago. Those refrigerants did not have big miscibility/sollubility problems with MO, as they were HCFC's.

    The problem now, is that the new substitute gases, such as R422D are mostly HFC's blends(around 97%), so, an oil change should be recommended. Otherwise, there will be oil return problems. Sometimes these problems arise in a few minutes, some other they show up in 1 year.

    Regards,

    Nando.
    I agree with you. An oil change should be made, specially if the plant has branches and complexity. But if it's a simple plant without that and no risers then there is no necessity of change oil, however a change is always better.

    Nando, R422D is also a drop in.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: R422d

    Quote Originally Posted by Sandro Baptista View Post
    I agree with you. An oil change should be made, specially if the plant has branches and complexity. But if it's a simple plant without that and no risers then there is no necessity of change oil, however a change is always better.

    Nando, R422D is also a drop in.
    Totally agree Sandro, the complexity and design of the plant might give problems or minimize/postpone them.

    I meant that the gases that did substitute R12 were called "drop ins", because it was as as easy as changing the gas (pick up the old one, drop in the new one) and so these new ones have been so called, but now, some more operations should be done, such as the oil change, i.e. That is why I said the new blends should not be considered as drop ins, since HFC's are not miscible at all with MO.

    Regards,

    Nando.

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: R422d

    ok. I agree with you.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Sep 2012
    Location
    the Netherlands
    Posts
    2
    Rep Power
    0

    Re: R422d

    Hi all,

    I am a new member and therefor not sure if I post this question in the right thread.

    A client of us has several WCU's currently running on R22, but would like to replace this with R427a. This to comply to the phase out regulation against the lowest possible costs.
    I would like to know if someone has experience with the relative new drop-in refrigerant R427a.

    What is the effect on the cooling capacity, COP, the pressures, (low) part load operation, etc.? Are there better alternatives?


    Best regards,

    JR

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: R422d

    Leaking seals are not the result of the oil not changed but of the type of refrigerant used. Wether you chanegd the oil or not, the problem with the seals will stay the same and this is becauser r22 tends to expand the seals and the 'drop-ins' shrink those again.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: R422d

    Quote Originally Posted by Peter_1 View Post
    Leaking seals are not the result of the oil not changed but of the type of refrigerant used. Wether you chanegd the oil or not, the problem with the seals will stay the same and this is becauser r22 tends to expand the seals and the 'drop-ins' shrink those again.
    I would say that is the combination pair oil-refrigerant, don't you agree?
    To make progress is never good enough, I want to do better and better and better