Results 1 to 10 of 10
  1. #1
    Join Date
    May 2012
    Location
    USA
    Posts
    1
    Rep Power
    0

    Reusing refrigerant from recovery bottles



    I am wondering about cleaning refrigerant thats been recovered from a system to be reused in other systems. Someone told me all the refrigerant they recover they clean with a filter drier and through some somewhat simple process he puts all his refrigerant in larger tanks.

    Just wondering if anyone knew of how this process works, what i need to do.

    sorry i can explain more of it.


    BTW first time posting...



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Reusing refrigerant from recovery bottles

    Most recovery machine manufacturers make cleaning kits to fit their machines.

    Generally, as you suggest, filter/driers and oil separators ect.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    154
    Rep Power
    16

    Re: Reusing refrigerant from recovery bottles

    Most of the time I pump the refrigerant through a drier to a storage bottle, then put it back in the system it came from. One for R22, another for R134A. When I start with other refrigerants I will have to get extra bottles for each one. Extra make up refrigerant comes from the bottle, as scrapped systems ( that have not lost all to a leak, but where the compressor is tired, but still trying to operate with a coil that is pipe only and no fins) get the same treatment before they meet Mr angle grinder and make the last boat trip to Ghangzhou.

  4. #4
    Join Date
    Jan 2010
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: Reusing refrigerant from recovery bottles

    Most recovery machine will remove some moisture and oil but the key is which refrigerant you are recovering, single refrigerants like R22 and R134A don't have a problem going out of spec but some of the new blends are quite unstable like R422D which contains 3.4% hydrocarbon to help with oil return some of these refrigerants can very easily go out of spec and once that happens it is no longer the refrigerant it used to be and will perform differently

  5. #5
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Reusing refrigerant from recovery bottles

    Quote Originally Posted by superslim007 View Post
    Most recovery machine will remove some moisture and oil but the key is which refrigerant you are recovering, single refrigerants like R22 and R134A don't have a problem going out of spec but some of the new blends are quite unstable like R422D which contains 3.4% hydrocarbon to help with oil return some of these refrigerants can very easily go out of spec and once that happens it is no longer the refrigerant it used to be and will perform differently
    Done it before, all we did was put a filter/drier in-line with the reclaim machine into a clean reclaim bottle. Just be careful with blends as he says ^^^

    J

  6. #6
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Reusing refrigerant from recovery bottles

    Quote Originally Posted by jdunc2301 View Post
    Done it before, all we did was put a filter/drier in-line with the reclaim machine into a clean reclaim bottle. Just be careful with blends as he says ^^^

    J
    The filter drier will remove partially the moisture, but you need a liquid separator to remove the oils(acids) as well, otherwise, the recovered gas is a residue.

    Regards,

    Nando.

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Reusing refrigerant from recovery bottles

    Hi ash
    This was ten years ago on the last phase out of the good refrigerants. I worked for a chiller specialist & used a giant still to clean R11 & R123, it may have been used for other refrigerants. The onus here would (no should) be that all refrigerant is returned to the manufacturer. The or some of the ingrediants could be seperated from recovered refrigerant. Certain ingrediants sepeate in a still at a given temperature, pressure & flow rate. Stills are great for making booze too.

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Reusing refrigerant from recovery bottles

    Quote Originally Posted by Fri3Oil System View Post
    The filter drier will remove partially the moisture, but you need a liquid separator to remove the oils(acids) as well, otherwise, the recovered gas is a residue.

    Regards,

    Nando.
    it doesnt clean it correct, have done it on systems when only replacing a single component or a small leak.

    J
    Last edited by jdunc2301; 21-06-2012 at 01:43 PM.

  9. #9
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Reusing refrigerant from recovery bottles

    Quote Originally Posted by jdunc2301 View Post
    it doesnt clean it correct, have done it on systems when only replacing a single component or a small leak.

    J
    Do you know the quantity in ppm's of impurities/dirt/water you got?

  10. #10
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Reusing refrigerant from recovery bottles

    Quote Originally Posted by Fri3Oil System View Post
    Do you know the quantity in ppm's of impurities/dirt/water you got?
    No..its irrelevant on the small stuff im dealing with... eg:

    Perfectly healthy working system having a pressure switch replaced due to a small amount of corrosion, reclaiming and charging with virgin becomes an affordability issue nowadays...if in doubt rip it out and charge with virgin...

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •