Thread: pipe blockage
    Apr 2012
    Iraq
    30
    614
    11
    pipe blockage
    hi
    when an ac unit is encountering leakage it must be welded and recharges
    some times during recharge ablockage in the capillary is happern or in evaporater
    so i have to discharge ***** and clean system by r22
    so could any body learn why blockage happen
    how to evade it
    how to open blockage
    Oct 2007
    manchester
    44
    5,707
    Re: pipe blockage
    use a vac pump and torr gauge-also purge with nitrogen whilst repairing-good luck:d
    Apr 2012
    Iraq
    30
    614
    11
    Re: pipe blockage
    thank you
    i made vaccum to the system
    by manifold gauge
    could explain meaning of torr gauge
    Oct 2007
    manchester
    44
    5,707
    Re: pipe blockage
    http://www.google.co.uk/search?q=tor...w=1213&bih=589
    pics of torr gauge
    you should change your vac pump oil frequently
    the gauge indicates moisture level in the system- gauge should be fitted at the farthest point from the vac pump but usually thats not practical- once your gauge drops to less than 2 torr,shut off the pump and you will see the gauge move after 30mins to show moisture is still present in the system. continue vaccing until the gauge stays at 2 torr with the vac pump shut off- if not then add nitro and re vac system- this will remove moisture from the system-good luck
    Apr 2012
    Iraq
    30
    614
    11
    Re: pipe blockage
    thank you man
    Oct 2007
    manchester
    44
    5,707
    Re: pipe blockage