    1000 m piping is really possible in VRF



    In Multi V III, VRV III, City Multi - Refrigerant Total Pipe Length is 1000 m.

    Such pipe length is possible to connect, when they have first Y Joint to Farthest Indoor unit is 40 m.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 1000 m piping is really possible in VRF

    I think you mean 100m?

  3. #3
    Join Date
    Feb 2008
    Location
    UAE
    Posts
    13
    Rep Power
    0

    Re: 1000 m piping is really possible in VRF

    No Total Pipe Length of 1000 m (Thousand)

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 1000 m piping is really possible in VRF

    Where did you get this information from? I'm intreged

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: 1000 m piping is really possible in VRF

    vrv3 heat recovery
    with a maximum of 165mtr i think its a translation error

    Equvalent pipe length between outdoor unit (*2) and idoor unit
    190m (Note 1)
    (Assume eqivalent pipe length of REFNET joint to be 0.5m, that of REFNET header to be 1m, that of BSVQ100, 160 to be 4m, that of BSVQ250 to be 6m for calculation purposes)
    Total piping length from outdoor unit (*2) to all indoor unit
    1000m
    Actual pipe length from first outdoor unit multi connection piping kit to outdoor unit
    10m
    Equivalent pipe length from first outdoor unit multi connection piping kit to outdoor unit
    13m
    Actual pipe length from first refrigerant branch kit (either REFNET joint or REFNET header) to indoor unit
    40m (Note 2)
    Example 8 : b + c + d + e + s
    40m
    Difference in height between outdoor unit and indoor unit (H1)
    50m (Max 40m if the outdoor unit is below)
    Difference in height between adjacent indoor units (H2)
    15m
    Difference in height between adjacent outdoor units (H3)
    5m
    Outdoor unit
    r
    10m
    (Equivalent length
    13m)
    u + s
    10m
    (Equivalent length
    13m)
    u + t
    10m
    (Equivalent length
    13m)
    Example 6 : b +
    40m
    Last edited by install monkey; 21-05-2012 at 08:35 PM. Reason: didnt mention the system

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 1000 m piping is really possible in VRF

    Yeah, it's possible. Working? I doubt it.

  7. #7
    Join Date
    Feb 2008
    Location
    UAE
    Posts
    13
    Rep Power
    0

    Re: 1000 m piping is really possible in VRF

    I couldn't understand the above example?

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: 1000 m piping is really possible in VRF

    A citi multi Y series can have a total pipe lenght (one way) of 3280ft which is 999.74 mtrs.
    BUT THAT DOES NOT MEAN YOU CAN HAVE AN INDOOR UNIT 1000MTRS AWAY FROM THE OUTDOOR.
    Cheers
    Stu