Results 1 to 22 of 22
  1. #1
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    High superheat but major frosting on compressor



    I have a system which is showing a low suction pressure ( -32 deg c sat )
    And a high super heat of 20 deg c
    But the compressor is showing major frosting as if liquid flood back and even Sticky to touch , temp at compressor inlet 8 deg c
    The evap coil isn't showing any real signs of frosting and the controlled space at -10 deg c and air On off Td is low
    There seems to be a lot of oil carried in the system , system is R422d

    I'm just confused as to why so much frosting at this temp ?

    Any help or advise welcome
    Thanks



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: High superheat but major frosting on compressor

    Sounds like its low in refrigerant in theory you shouldn't have frost where liquid is present Low td also
    the same as is high superheat

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: High superheat but major frosting on compressor

    kfjoe,
    It has been said numerous times in other post, do you have a liquid/suction line heat exchanger
    that could be internally fractured?
    Some heat exchangers are obvious, while others are built in fan casing of evaporator.
    Measure superheat at evaporator bulb to see if its same as compressor, if not its something downstream of TX bulb.

  4. #4
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: High superheat but major frosting on compressor

    No heat exchanger , superheat at bulb 20 and at compressor 18
    It's just the amount of frost and how rapid on compressor that I find strange

  5. #5
    Join Date
    Dec 2010
    Location
    ireland
    Age
    46
    Posts
    62
    Rep Power
    15

    Re: High superheat but major frosting on compressor

    replace exspansion valve and check the size orofice.... or someone might have screwed open the valve to the last... maybe try adjusting valve to get proper superheat in coil

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: High superheat but major frosting on compressor

    Is the compressor surface temperature below the ambient dew point?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: High superheat but major frosting on compressor

    Yes it's at -8 , so I understand it will frost
    It's just the amount of frosting and the sticky to touch as if it's liquid
    As there seems to be a lot of oil around the system , I'm wondering if this has some bearing on readings etc

  8. #8
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: High superheat but major frosting on compressor

    1) Maybe you should measure superheat at hours of low thermal load. The system could be hunting then.

    2) Check your oil separator, it could be condensing significant amounts of refrigerant. You'll see foaming when the float opens.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  9. #9
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: High superheat but major frosting on compressor

    what is your suction pressure?
    what is your discharge pressure?
    i would suspect also that if the system is on R422d and it is a low temp aplication it should have liquid injection?
    is the liquid injection control faulty hence too much liquid in the suction.
    your only as good as your last job

  10. #10
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: High superheat but major frosting on compressor

    Quote Originally Posted by cold.man View Post
    what is your suction pressure?
    what is your discharge pressure?
    i would suspect also that if the system is on R422d and it is a low temp aplication it should have liquid injection?
    is the liquid injection control faulty hence too much liquid in the suction.
    You could be onto something here.. starved system = high superheat=high discharge temp = liq injection...

  11. #11
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: High superheat but major frosting on compressor

    compressor to strong for the evaporator

  12. #12
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: High superheat but major frosting on compressor

    Thanks for all the replies guys

    The superheat isn't as high as I thought , it's 11 deg c
    Liquid injection is fine
    I have a poor TD across the coil and a low evaporating temperature but airflow is good
    No oil separator on this system
    There is a lot of oil in the system though and you see this when taking off the low side gauge line
    I'm wondering if the oil is effecting the evaporator and giving it its poor TD ?

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: High superheat but major frosting on compressor

    What oil is it running on? POE or mineral? POE would be better with R422D.

    What was fault you were called to fix?

    Has the system ever worked since being converted to R422D?
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: High superheat but major frosting on compressor

    as monkey spanners said POE is better with R422d
    If the system has been retrofitted from R22 and was on mineral oil change the oil to POE or at least a 80% POE 20% mineral oil mix if the compressor is still the same.
    oil return with minerial oil on R422d is poor, does the system have an oil saftey switch?
    What set up do you have for the oil you say there is no oil sep, what do you have?
    your only as good as your last job

  15. #15
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: High superheat but major frosting on compressor

    AB (Alkylbenzene) Oil is also Miscible with R422D and mixes with the existing mineral oils pre retrofit.

  16. #16
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: High superheat but major frosting on compressor

    It is Poe
    And it is an r22 retrofit
    Fault was the old not achieving temperature
    Has it ever worked properly ? Maybe not since being converted , but I didn't do the conversion
    There is no oil sep at all , close coupled system relying on velocity for return
    I think you may have something with the oil , I don't know how many oil changes etc were done
    I think I will test for mineral oil , but with r422d supposed to work with mineral oil and with a percentage of Poe added im confused why

  17. #17
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: High superheat but major frosting on compressor

    -32°C suction + 11° superheat = return gas at -21 not +8 like in your original post.

    When you measure low temperatures in high ambient you should insulate your probe and up and low river so that your sensor and tube take the gas temperature.

    -21°C gas would explain the ice without liquid refrigerant.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  18. #18
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: High superheat but major frosting on compressor

    Oh and you should pay attention at defrosts if the oil level goes up in the compressor, your evaporator could be logging too much oil.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  19. #19
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: High superheat but major frosting on compressor

    Loose fins of evaporator ???????? Not enough heat transfer .

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: High superheat but major frosting on compressor

    Evap air in temp
    Evap air out temp
    Low side pressure/saturated suction temp
    Suction line temp at TXV bulb

    Cond air in temp
    Cond air out temp
    High side pressure/saturated condensing temp
    Liquid line temp at sight glass

  21. #21
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: High superheat but major frosting on compressor

    Sorry for the late reply, not been on lately
    Appreciate all the replies and help

    Evap air on -10
    Evap air off -13
    Low side pressure 15 psig
    Suction line temp at bulb -10

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: High superheat but major frosting on compressor

    The air flow is okay and the superheat is high. That's about all we can tell without a full set of readings.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •