    Chiller barrel replacement?



    I have a 150 ton chiller with air cooled condenser that has a 24 year old barrel. The water treatment tests good.ASHRAE gives the average life of a barrel of 24 years. We have not done an eddy current test. I think the baffles inside may be corroded because I cannot get my Delta T more than 5 degrees, no matter how I try to balance the water flow. I am thinking of putting this in our budget for next year because if it goes out, the building has 5 stories of tenants and the windows don't open. I replaced one compressor and rebuilt the other one 2 years ago. Any suggestions.



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Chiller barrel replacement?

    michaele, wether its next year or the year after, its going be changed , it cannot last for ever , are you going to change it to air cooled aswell ? sedgy ,

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chiller barrel replacement?

    Have you thought about fitting a brazed plate heat exchanger instead?

  4. #4
    Join Date
    May 2010
    Location
    U.S.
    Age
    68
    Posts
    18
    Rep Power
    0

    Re: Chiller barrel replacement?

    Quote Originally Posted by sedgy View Post
    michaele, wether its next year or the year after, its going be changed , it cannot last for ever , are you going to change it to air cooled aswell ? sedgy ,
    I hadn't considered converting to a DX coil instead of a barrell if that is what you mean. It is interesting to think about. I don't have the knowledge to design the coils for the capacity or staging. The chilled water system has given us good service over the years.

  5. #5
    Join Date
    May 2010
    Location
    U.S.
    Age
    68
    Posts
    18
    Rep Power
    0

    Re: Chiller barrel replacement?

    Quote Originally Posted by frank View Post
    Have you thought about fitting a brazed plate heat exchanger instead?
    I have not thought about that either. There again, I would have to research this. Could it be more efficient or cost effective?

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chiller barrel replacement?

    Here's a link http://www.brazetek.com/

  7. #7
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Chiller barrel replacement?

    Comparing PHE with S&T they are more efficient in certain aspects like much larger area/volume ratio, weight full less than 50%, use 1/10th water, less refrigerant, about the same width, 1/5th in length, about twice as tall though and very little service space, less fouling, no stagnation points.

    They do have some drawbacks, the one I miss most is literature. There is not a TEMA for PHEs. Less rugged, You need better filters, water-side pressure drop is larger, flow requirements more stringent. BPHE cannot be fixed.

    But anyway Frank´s idea is very good.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Chiller barrel replacement?

    Have you checked the partitions in water boxes, could be a problem of bypass giving low delta T.
    A lot of S&T vessels have plastic baffles internally on the water side.