09-05-2012, 10:11 AM #1
suction pressure
Hi
Can some please give me an insight on the causes of high suction pressures in an NH3 screw compressor when the system is not on load? any other literature on the operation of NH3 refrigeration system will be highly appreciated
thanks
ogola
-
09-05-2012, 10:35 PM #2
Re: suction pressure
Not knowing the design of the system or putting my hands on it, I have 3 suggestions.
1. Could it be high suction temp? maybe a unit's hot gas defrost valve is leaking by or may have a unit in defrost when all the liquid solenoids are closed.
2. Talking a Reciprocating compressor. If false loading it, load goes away, discharge gets diverted to the suction.
3. If a screw and economized, may have a bad regulator on the economizer line.
Just a few that I could think of.
Good luck!
-
14-05-2012, 09:38 AM #3
Re: suction pressure
Hi, Ogolan
welcome to RE forums ...
Can you, please, clarify above text in bold ....
1. compressor is not working ... stopped
2. or compressor is working at low capacity
3. how high is that "high" suction pressure
4. in the same system you have some other running compressor/s
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
23-05-2012, 09:25 AM #4
Re: suction pressure
Also check the discharge chek valve...