Results 1 to 10 of 10
    Mar 2012
    United Kingdom
    36
    63
    Thumbs up Carrier 30sz-027-901v-ee
    IMAG0021.jpg Hi guys anyones know how much oil should I fill in to this compressor ? I guessing 7,5 liters is that Ok ????
    Thanks for any reply .
    P.S 20 kg of R 407A is right charge . . . ?
    Oct 2007
    manchester
    43
    5,709
    Re: Carrier 30sz-027-901v-ee
    couldnt find info on a 30sz
    Since different refrigerants (CFC, HCFC, or HFC)
    require specific oils (mineral, alkylbenzene, or
    polyolester [POE]), Carlyle ships most new and
    service compressors without oil. The oil level for
    06CC size 16 to 37 Cfm compressors and all 06D
    compressors should be at 1/4 to 3/4 of the sight
    glass. The oil level for 06CC size 50 to 99 Cfm
    compressors and all 06E compressors should be
    at 1/8 to 3/8 of the sight glass.
    See Sections 3.6
    and 3.7, pages 69 to 72 for the proper Carlyle
    approved oils for the selected refrigerant. Oil
    should be added through the recommended oil fill
    connection ports on the compressor as identified
    in the figures in secton 2.5.
    Once the compressor system has been running for
    at least 24 hours, the most accurate oil levels are
    observed when the compressor is off. Oil levels in
    the sight glass can be affected by the rotation of the
    running gear.
    OPERATING OIL LEVELS
    06CC (16 TO 37 CFM) AND 06D
    3/4 (MAX)
    1/4 (MIN)
    06CC (50 TO 99 CFM) AND 06E
    3/8 (MAX)
    1/8 (MIN)
    Mar 2012
    United Kingdom
    36
    63
    Thaaaanks You dude where from have U got this info I was looking everywhere . . . .
    Oct 2007
    manchester
    43
    5,709
    ill e mail u the o6e service book
    Oct 2007
    manchester
    43
    5,709
    check ur e mail
    Mar 2012
    United Kingdom
    36
    63
    I did Thank You very much really appreciate your time ! ! ! Btw I done that job its working fine just one question about oil level . I top it up compressor with 1 liter new oil RH 68 L and Its slightly more then maximum ... it is so dangerous for bearing if compressor run only 5 min ??? Dialog-pro doesnt schow any error anyway yet .
    Thanks guys .
    Oct 2007
    manchester
    43
    5,709
    slightly more than maximum- is that 3/8-1/2 of your oil sight glass-you need to moniter the oil level for 24hrs , ensuring crankcase heaters are working.
    as for the 5 mins of operation- maybe increase setpoint maybe widen the deadband so it runs for longer.
    Mar 2012
    United Kingdom
    36
    63
    Crankcase heater is working and is nearly flood it I would say about 90 percent but I just watched 4 1 hour after new charge ... Its old compressor so I dont care and is not working so often ... Really thanks 4 yours skills i just learning about refrigeration more and more cos I like it a lot .
    Have Nice evening sorry 4 my English lol
    Oct 2007
    manchester
    43
    5,709
    being on here means i dont have to talk to the mrs
    found some info for you- will e mail you
    Feb 2012
    5
    Hello I.M., I am new to this site and trying to learn how to get around where i want to be. Came across this thread and would like to ask you if you would not mind sending a copy of the o6e service book to my email? I really would appreciated. Thanks in advance