    mr slim p8 error code



    anybody got any ideas with this 1...

    set up = 4 x mitsi elec mr slim large cassettes
    indoor - PLH - 5GKHV
    outdoor - PUH - 5YK2

    all run off 1 remote control...

    3 units run fine in both heating and cooling...

    unit no 2.... doesnt kick in....no leds on pcb outsite...compressor sounds fine...

    error code on remote is p8

    misti elec tech guy said "check the outdoor board"

    i thought i was playing give us a clue...

    asked again for bit more details - "check the outdoor board"

    now interestingly, the bypass solenoid valve is quite burned out, il post the pics in abit...

    and the liquid reciever is quite burned also...

    any 1 got any ideas please ?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: mr slim p8 error code

    Hi Krups

    P8 means "Abnormality in Outdoor Unit" that's why the tech guy has told you to look at the outdoor unit.

    Possible causes
    1 Wrong wiring of Indoor/Outdoor connection
    2 Reverse Phase
    3 Protection Device operated
    4 damaged Outdoor coil thermistor

    Areas to check

    1 Check continuity of the interconnect wiring - look for breaks (I've had it where rats have chewed the wiring before )

    2 Check the phase rotation - has any work been done on the unit mains wiring?

    3 Has any safety activated? Compressor klixon? LP switch? HP switch, Fan overload? etc.

    4 Measure the resistance of the coil sensor

    If you are still struggling then give Mitsi Technical a ring 08703000300

  3. #3
    Join Date
    Jul 2003
    Location
    leicester
    Age
    42
    Posts
    122
    Rep Power
    21

    Re: mr slim p8 error code

    hi, just found this thread aswel that relates to it..

    http://www.refrigeration-engineer.co...read.php?t=877

    i noticed u said here, it could be caused by hp fault, more often than not caused by dirty indoor filters,

    well when i got here, the filters were some of the worst iv seen, had not been cleaned in at least 3 years i was told...

    and the system had been left on heating for the last few months due 2 weather..

    also as no leds are lit...
    surely that can rule out check point 1 on ur list above ?

    check point 2 - will do that.

    check point 3 - not sure - also needs looking at.

    check point 4 - what readings am i looking for ?

    btw this is 3 ph.

    could it be a faulty pcb ? as no leds light up ?

    i notice alec posted this -

    Is it a 3phase condensing unit?If so p8 can refer to phase imbalance or rotation direction, try swapping two phases.Inside of condensing unit cover should detail led faults, are any flashing?Could also be loss of charge or faulty boards

    also - as that soleniod is extremely melted...would that be a culprit ? what can cause that to happen ?

    @ aiyub - u never did post how you got on...

  4. #4
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: mr slim p8 error code

    P8 is not just an outdoor unit fault!!!
    It is triggered 15 mins after a heating/ cooling signal has been sent to the outdoor unit and there is less than
    5oC differential between room sensor and indoor coil sensor. Sensor errors can also produce a P8

    Anyway most P8's occur when there is a power cut on site - outdoor unit thinks its lost a phase so shuts down. To reset just turn outdoor isolators off to all outdoor units, wait 10 secs, then switch back on again.

    If the outdoor unit has a fault on it you'll find a list of led sequences on the inside of the cover-
    On old R22 systems there are eight (one will be flashing), on 407c/410a systems there is a red and green led. If you have missing phase defect reset power, if you have th4 (discharge) too high it is likely that you have a leak- these are the 90% of Mr slim probs that i come accross

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: mr slim p8 error code

    The solenoid coil? If the coil is taken off the valve stem then it can't dissipate it's heat and can burn out. Also, if the valve is running for any length of time extremely hot due to high discharge pressures/temps then the same thing can happen.
    Of course it could just be that the coil is knackered

    My guess is that the indoor filters have been heavily contaminated and the compresor has been running hot leading to a HP trip.

    It's probably nothing to do with the phase rotation as the other units are working. You can swap the outdoor coil sensor with one of the other units to prove that it's working and it's fairly simple to do a continuity test on the wiring.

  6. #6
    Join Date
    Jul 2003
    Location
    leicester
    Age
    42
    Posts
    122
    Rep Power
    21

    Re: mr slim p8 error code

    it is an R22 system...

  7. #7
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: mr slim p8 error code

    Quote Originally Posted by Krups
    unit no 2.... doesnt kick in....no leds on pcb outsite...compressor sounds fine...
    Does the compressor work or not??
    do you know that you should never push contactors in on a misti / daikin / tosh etc.

    to test outdoor board you can check that you have 18v ac on the interconnecting wiring - this shows that you have an output at least. All boards have fuses and ZNR's check them!!

    If you push sw1 (i think) you will see the last led fault code- if the sun is shining on unit you may need to get in close to see which led is flashing

  8. #8
    Join Date
    Jul 2003
    Location
    leicester
    Age
    42
    Posts
    122
    Rep Power
    21

    Re: mr slim p8 error code

    didnt know that you should never push the contactors, was taught on the job, that its fine...
    just out of curiosity,y is it there then ?

    i pushed sw1, and sw2....
    but nothing happened...not sunny dwn here in leicester im afraid...

  9. #9
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: mr slim p8 error code

    on all mitsi/ daikin there is tape over contactor that say "don't push in" you must have torn this to push in.

    I think that you may get back feed that can effect pcb etc. Also on some models pcb controls compressor rotation (i think) so you may damage it!!

    It is alright to push in contactors to most other fridge stuff, but japanese ac units with pcb's are a no no!

    I still think you may want to reset power to clear fault then put guages on if unit runs, get yourself a solenoid magnet to test the valve. Also if site (or unit ) has lost a neutral it will blow ZNR (blows at 550V) make sure this hasn't blown (it looks like a green leaf) -if it has check neutral and replace outdoor pcb

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: mr slim p8 error code

    Quote Originally Posted by aeb200
    Does the compressor work or not??
    do you know that you should never push contactors in on a misti / daikin / tosh etc.
    It's always the first thing I do to see if compressor is still running and if there is power supply to the unit.
    The only reason I see is that the compressor runs then in reverse, that's all.
    Back feed to the PCB??? You're only making a contact on the main leads to the compresser.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: mr slim p8 error code

    Quote Originally Posted by Krups
    i pushed sw1, and sw2....
    but nothing happened...not sunny dwn here in leicester im afraid...
    SW2 shows fault codes, SW1 clears fault codes I think, get them the wrong way around and the fault could be cleared before you get a chance to see it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Jul 2003
    Location
    leicester
    Age
    42
    Posts
    122
    Rep Power
    21

    Re: mr slim p8 error code

    oops lol iv pressed them both neways...
    but the leds didnt work neways...
    so ....
    guess it never made a diff ?

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: mr slim p8 error code

    P8 was nearly always a refrigerant leak for me..

    cheers

    richard

  14. #14
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: mr slim p8 error code

    HI Krups ,
    If there are no led's on the outdoor check the transformer. they go down reg.
    regards
    T

  15. #15
    Join Date
    Dec 2005
    Location
    Angus, Scotland
    Age
    50
    Posts
    14
    Rep Power
    0

    Re: mr slim p8 error code

    Lo all...

    Sparky in my first life doing a/c ..refridg now for almost 10 years and i have never understood why it is so tabbooooo "NOT" to push that contactor on some splits...
    must agree with peter in that it is the first thing i usually do also...... how else do you tell if the comp is running especially if the units are a 20 min hike away from each other...........

    sorry to deviate from the original topic

    best advice i can give for a Mr Slim is bin it and fit a daikin......


  16. #16
    Join Date
    May 2009
    Location
    Montreal
    Age
    62
    Posts
    34
    Rep Power
    0

    Re: mr slim p8 error code

    If the indoor filters were clogged, the pressure would go down because of insufficient air going over the evaporator causing it to freeze, P8 error code is truely an outdoor unit problem, such as: thermistor defective, lost of power dirty condensor and so forth.

  17. #17
    Join Date
    Oct 2008
    Location
    Australia
    Posts
    210
    Rep Power
    16

    Re: mr slim p8 error code

    Would of been handy 4 years ago lol

  18. #18
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: mr slim p8 error code

    ^ and ignoring the heat pump function.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  19. #19
    kenayd's Avatar
    kenayd Guest

    Re: mr slim p8 error code

    Hi
    I have a puh-5yk and after we had a black the p8 error code showed up. I have checked everything and it is still showing up.
    How do i fix it.

  20. #20
    kenayd's Avatar
    kenayd Guest

    Re: mr slim p8 error code

    Sorry guys that was we had a black out.lol

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: mr slim p8 error code

    fuses on outdoor pcb 20mm glass fuses.
    normally led 8 lit constantly for crankcase heater if the compressor isnt operating.
    if a coil has burnt out then that is going to take out the fuses on pc.
    check 12vdc on 1 and 2 for compressor signal
    1 and 3 reversing valve

  22. #22
    Join Date
    Feb 2011
    Location
    england
    Age
    49
    Posts
    10
    Rep Power
    0

    Re: mr slim p8 error code

    Hi mate Ive had this error code before and its a bad one ! Basiclly P8 comes up when the indoor evaporator does nt read any temperature differential change over 9 mins so Have you checked Gas Charge ??? You say compressor is ok but No lights on the Board ? they Can be very tiny lights and make sure you roll a tube of paper to see them as this creates a bit of darkness as you look down the tube . Best put the Gauges on See if you got head/suction pressures Before you do that Check indoor coils for Cooling to 10 deg offset to controller. You should get some change before 9 mins is up :-) Its usually compressor or Gas or yeah Board :-)

  23. #23
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: mr slim p8 error code

    some mitsi r22 units have electric heaters in to boost output.u can see them around the inside of the evap coil.they have an auto reset overheat klixon and are powered via a relay near the power a n e terminals.if the filters are heavily clogged then remove the indoor fan blade and chemically clean the evap coil with a garden sprayer to improve performance.

  24. #24
    Join Date
    Jan 2009
    Location
    london
    Posts
    52
    Rep Power
    16

    Re: mr slim p8 error code

    Just a post to agree with Big Bear.

    Had P8 fault the other day, Found compressor running, but not pumping. 1 Week out of warranty. Replaced compressor and all good!

Similar Threads

  1. mitsubishi mr slim master and slave
    By r600a-bang in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 10:24 AM
  2. Mr Slim
    By Abe in forum Air Conditioning
    Replies: 7
    Last Post: 25-01-2006, 09:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •