Results 1 to 24 of 24
    Jul 2003
    leicester
    42
    122
    mr slim p8 error code
    anybody got any ideas with this 1...
    set up = 4 x mitsi elec mr slim large cassettes
    indoor - PLH - 5GKHV
    outdoor - PUH - 5YK2
    all run off 1 remote control...
    3 units run fine in both heating and cooling...
    unit no 2.... doesnt kick in....no leds on pcb outsite...compressor sounds fine...
    error code on remote is p8
    misti elec tech guy said "check the outdoor board"
    i thought i was playing give us a clue...
    asked again for bit more details - "check the outdoor board"
    now interestingly, the bypass solenoid valve is quite burned out, il post the pics in abit...
    and the liquid reciever is quite burned also...
    any 1 got any ideas please ?
    5,668
    Re: mr slim p8 error code
    Hi Krups
    P8 means "Abnormality in Outdoor Unit" that's why the tech guy has told you to look at the outdoor unit.
    Possible causes
    1 Wrong wiring of Indoor/Outdoor connection
    2 Reverse Phase
    3 Protection Device operated
    4 damaged Outdoor coil thermistor
    Areas to check
    1 Check continuity of the interconnect wiring - look for breaks (I've had it where rats have chewed the wiring before )
    2 Check the phase rotation - has any work been done on the unit mains wiring?
    3 Has any safety activated? Compressor klixon? LP switch? HP switch, Fan overload? etc.
    4 Measure the resistance of the coil sensor
    If you are still struggling then give Mitsi Technical a ring 08703000300
    Nov 2005
    Southampton
    54
    P8 is not just an outdoor unit fault!!!
    It is triggered 15 mins after a heating/ cooling signal has been sent to the outdoor unit and there is less than
    5oC differential between room sensor and indoor coil sensor. Sensor errors can also produce a P8
    Anyway most P8's occur when there is a power cut on site - outdoor unit thinks its lost a phase so shuts down. To reset just turn outdoor isolators off to all outdoor units, wait 10 secs, then switch back on again.
    If the outdoor unit has a fault on it you'll find a list of led sequences on the inside of the cover-
    On old R22 systems there are eight (one will be flashing), on 407c/410a systems there is a red and green led. If you have missing phase defect reset power, if you have th4 (discharge) too high it is likely that you have a leak- these are the 90% of Mr slim probs that i come accross
    Jul 2003
    leicester
    42
    122
    hi, just found this thread aswel that relates to it..
    http://www.refrigeration-engineer.co...read.php?t=877
    i noticed u said here, it could be caused by hp fault, more often than not caused by dirty indoor filters,
    well when i got here, the filters were some of the worst iv seen, had not been cleaned in at least 3 years i was told...
    and the system had been left on heating for the last few months due 2 weather..
    also as no leds are lit...
    surely that can rule out check point 1 on ur list above ?
    check point 2 - will do that.
    check point 3 - not sure - also needs looking at.
    check point 4 - what readings am i looking for ?
    btw this is 3 ph.
    could it be a faulty pcb ? as no leds light up ?
    i notice alec posted this -
    Is it a 3phase condensing unit?If so p8 can refer to phase imbalance or rotation direction, try swapping two phases.Inside of condensing unit cover should detail led faults, are any flashing?Could also be loss of charge or faulty boards
    also - as that soleniod is extremely melted...would that be a culprit ? what can cause that to happen ?
    @ aiyub - u never did post how you got on...
    5,668
    The solenoid coil? If the coil is taken off the valve stem then it can't dissipate it's heat and can burn out. Also, if the valve is running for any length of time extremely hot due to high discharge pressures/temps then the same thing can happen.
    Of course it could just be that the coil is knackered
    My guess is that the indoor filters have been heavily contaminated and the compresor has been running hot leading to a HP trip.
    It's probably nothing to do with the phase rotation as the other units are working. You can swap the outdoor coil sensor with one of the other units to prove that it's working and it's fairly simple to do a continuity test on the wiring.
    May 2009
    Montreal
    If the indoor filters were clogged, the pressure would go down because of insufficient air going over the evaporator causing it to freeze, P8 error code is truely an outdoor unit problem, such as: thermistor defective, lost of power dirty condensor and so forth.
    Jul 2003
    leicester
    42
    122
    it is an R22 system...
    Nov 2005
    Southampton
    54
    Quote Originally Posted by Krups
    Does the compressor work or not??
    do you know that you should never push contactors in on a misti / daikin / tosh etc.
    to test outdoor board you can check that you have 18v ac on the interconnecting wiring - this shows that you have an output at least. All boards have fuses and ZNR's check them!!
    If you push sw1 (i think) you will see the last led fault code- if the sun is shining on unit you may need to get in close to see which led is flashing
    Oct 2003
    5,630
    Quote Originally Posted by aeb200
    It's always the first thing I do to see if compressor is still running and if there is power supply to the unit.
    The only reason I see is that the compressor runs then in reverse, that's all.
    Back feed to the PCB??? You're only making a contact on the main leads to the compresser.
    Dec 2005
    Angus, Scotland
    14
    Lo all...
    Sparky in my first life doing a/c ..refridg now for almost 10 years and i have never understood why it is so tabbooooo "NOT" to push that contactor on some splits...
    must agree with peter in that it is the first thing i usually do also...... how else do you tell if the comp is running especially if the units are a 20 min hike away from each other...........
    sorry to deviate from the original topic
    best advice i can give for a Mr Slim is bin it and fit a daikin......
    Jul 2003
    leicester
    42
    122
    didnt know that you should never push the contactors, was taught on the job, that its fine...
    just out of curiosity,y is it there then ?
    i pushed sw1, and sw2....
    but nothing happened...not sunny dwn here in leicester im afraid...
    Nov 2005
    Southampton
    54
    on all mitsi/ daikin there is tape over contactor that say "don't push in" you must have torn this to push in.
    I think that you may get back feed that can effect pcb etc. Also on some models pcb controls compressor rotation (i think) so you may damage it!!
    It is alright to push in contactors to most other fridge stuff, but japanese ac units with pcb's are a no no!
    I still think you may want to reset power to clear fault then put guages on if unit runs, get yourself a solenoid magnet to test the valve. Also if site (or unit ) has lost a neutral it will blow ZNR (blows at 550V) make sure this hasn't blown (it looks like a green leaf) -if it has check neutral and replace outdoor pcb
    11,025
    SW2 shows fault codes, SW1 clears fault codes I think, get them the wrong way around and the fault could be cleared before you get a chance to see it.
    Jul 2003
    leicester
    42
    122
    oops lol iv pressed them both neways...
    but the leds didnt work neways...
    so ....
    guess it never made a diff ?
    rbartlett's Avatar
    rbartlett Guest
    P8 was nearly always a refrigerant leak for me..
    cheers
    richard
    Jul 2005
    Ireland
    56
    164
    HI Krups ,
    If there are no led's on the outdoor check the transformer. they go down reg.
    regards
    T
    Oct 2008
    Australia
    210
    Would of been handy 4 years ago lol
    11,025
    ^ and ignoring the heat pump function.
    kenayd's Avatar
    kenayd Guest
    I have a puh-5yk and after we had a black the p8 error code showed up. I have checked everything and it is still showing up.
    How do i fix it.
    kenayd's Avatar
    kenayd Guest
    Sorry guys that was we had a black out.lol
    manchester
    5,639
    fuses on outdoor pcb 20mm glass fuses.
    normally led 8 lit constantly for crankcase heater if the compressor isnt operating.
    if a coil has burnt out then that is going to take out the fuses on pc.
    check 12vdc on 1 and 2 for compressor signal
    1 and 3 reversing valve
    Feb 2011
    10
    Hi mate Ive had this error code before and its a bad one ! Basiclly P8 comes up when the indoor evaporator does nt read any temperature differential change over 9 mins so Have you checked Gas Charge ??? You say compressor is ok but No lights on the Board ? they Can be very tiny lights and make sure you roll a tube of paper to see them as this creates a bit of darkness as you look down the tube . Best put the Gauges on See if you got head/suction pressures Before you do that Check indoor coils for Cooling to 10 deg offset to controller. You should get some change before 9 mins is up :-) Its usually compressor or Gas or yeah Board :-)
  23. #23
    manchester
    5,639
    some mitsi r22 units have electric heaters in to boost output.u can see them around the inside of the evap coil.they have an auto reset overheat klixon and are powered via a relay near the power a n e terminals.if the filters are heavily clogged then remove the indoor fan blade and chemically clean the evap coil with a garden sprayer to improve performance.
  24. #24
    Jan 2009
    london
    52
    Just a post to agree with Big Bear.
    Had P8 fault the other day, Found compressor running, but not pumping. 1 Week out of warranty. Replaced compressor and all good!
  1. mitsubishi mr slim master and slave
    By r600a-bang in forum Air Conditioning
    Last Post: 24-07-2006, 10:24 AM
  2. Mr Slim
    By Abe in forum Air Conditioning
    Last Post: 25-01-2006, 08:59 PM