    suction pressure



    Hi
    Can some please give me an insight on the causes of high suction pressures in an NH3 screw compressor when the system is not on load? any other literature on the operation of NH3 refrigeration system will be highly appreciated
    thanks
    ogola



  2. #2
    Join Date
    Apr 2009
    Location
    TEXAS
    Age
    49
    Posts
    28
    Rep Power
    0

    Re: suction pressure

    Not knowing the design of the system or putting my hands on it, I have 3 suggestions.

    1. Could it be high suction temp? maybe a unit's hot gas defrost valve is leaking by or may have a unit in defrost when all the liquid solenoids are closed.
    2. Talking a Reciprocating compressor. If false loading it, load goes away, discharge gets diverted to the suction.
    3. If a screw and economized, may have a bad regulator on the economizer line.

    Just a few that I could think of.
    Good luck!

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: suction pressure

    Hi, Ogolan

    welcome to RE forums ...

    Quote Originally Posted by Ogolan View Post
    Hi
    Can some please give me an insight on the causes of high suction pressures in an NH3 screw compressor when the system is not on load? any other literature on the operation of NH3 refrigeration system will be highly appreciated
    thanks
    ogola

    Can you, please, clarify above text in bold ....

    1. compressor is not working ... stopped
    2. or compressor is working at low capacity

    3. how high is that "high" suction pressure
    4. in the same system you have some other running compressor/s

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: suction pressure

    Also check the discharge chek valve...