    Question Starved Evaporator Troubleshooting?



    Hi everyone,

    I've got a reverse cycle A/C system which has an oversize condenser.

    In cooling it's great thanks to the big condenser. But in heating mode when the condenser become the evaporator, there comes problems.

    I have very low Evaporating temp (-28C), very low Suction pressure, very high SH (30K, although 2-TXV is set to minimum SH, wide open)

    What are the different ways to increase the evaporating temperature?

    The indoor side if fixed, I can not change a thing there.
    Things can be changed including outdoor airflow (which is currently quite high already, 670m3/h on high), outdoor coil size and tube configuration (can make it bigger or smaller or whatever tube arrangement), charge amount can also be change slightly (may have adverse effect because of relatively small indoor coil), can't fit a bigger TXV which is already oversize.

    Any comment is greatly appreciated.

    Thank you



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Starved Evaporator Troubleshooting?

    SOG? (Short of gas)
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Hey mate, Is there a blockage anywhere drier, txv? What are your condenser fans doing when in heating mode are they running.

  4. #4
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    desA, the indoor HX is quite small so I was hesitated to increase the charge amount. May push a little bit further and see if it sustains high load condition.

    cool_tech, small-non serviced system so no drier used, TXV was brandnew & it works perfectly in cooling mode. Cond Fan was high.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Starved Evaporator Troubleshooting?

    Fit outdoor fan control to maintain your pressures.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Starved Evaporator Troubleshooting?

    Are you sure the oversized condenser is designed to work as an evap? Can you post pictures?

    Does it initially work fine and after a while the pressure drops? If so it could be logging oil.
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  7. #7
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Brian_UK, do you mean higher airflow higher evap pressure/temp? My fan is a two speeds one and I switched between them.

    aramis, this is a custom made system. That's also why I mentioned the whole outdoor setup can be changed.

    What happen to the temps & pressures if I fit in a smaller outdoor coil (1/3 thinner) & maintain high, or even higher airflow? The supply side (Comp+ Indoor + TXV) is unchanged, if we just changed the demand, will there be any positive changes?

    If the pipe between TXV & outdoor coil inlet is un-insulated, any bad effect?

    It's quite hard to understand and predict the correlation between all the balance forces.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Starved Evaporator Troubleshooting?

    Uni.
    it is short of gas, you can theorize till the cows come home from what ever direction. The system is short of gas. As per DesA post.

  9. #9
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Thanks for posting Magoo, I'll push it to the upper limit today and will report back the result.
    Auckland, I'll come one day.

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Starved Evaporator Troubleshooting?

    "UNI", you said the a/c works "well" in cooling mode. What it the temperature difference across the evap coil?
    Air on vs air off. If it's in the range of 12 degrees c or better, in cooling mode, on medium fan speed, (with the room temperature above 25 C) then i might not be interested in the gas charge.
    Running in reverse cycle, with bugger all pressure, i would look at your expansion valve feed, as well as supply liquid temperature. Is the expansion valve and distributor heavily iced up? (Yes?)
    Do you have the correct size orifice in the valve? Not looking for you to fit a bigger valve, but maybe you have too small an orifice in the valve to make it work properly, in reverse cycle.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  11. #11
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    mikeref, Td approx 12-14C at 27C amb., high fan spd.
    I am not so sure how to change to orifice in the valve. It was factory fitted. The next size is ways to big for other mode & conditions. What about shortenning the spring? It's quite easy to open the assembly and refit it.

    Also, have just tried more charge, several steps up, not much improvement to the parameters if not the same.

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Starved Evaporator Troubleshooting?

    need a picture, or link to show me what valve you have out there on the condenser
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    You should have two TXV's, one at the outdoor coil and one at the indoor coil. Each of these should have a bypass line with a check valve in it. The arrow on the check valve should be pointed away from the coil. It sounds to me like a problem with the indoor check valve.

  14. #14
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Starved Evaporator Troubleshooting?

    hello all
    From what I think, the gas charge should be lower in operation in the heat pump, since the capacitor is larger.
    so I think that the expansion valve is not properly fed by the liquid causes of obstruction on the line.
    however it is possible to insert a reserve of liquid to ensure the two cycles of operation.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    In heat mode, the indoor coil is the condenser. The liquid from the indoor coil flows through the indoor check valve to the outdoor TXV. If the indoor check valve is stuck in the closed position, the liquid must flow backwards through the indoor TXV, severely restricting the flow.

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    You should also be aware that there are TXV's available which have the bypass/check valve built in. Scroll down to the bottom in this PDF:

    http://www.emersonclimate.com/Docume...re-article.pdf

  17. #17
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Gary & mikeref, I used the two (one) ways TXV as described in Emerson's article. Two different TXV & check valve would be too bulky & could bring along more assembly issues.
    Based on the datasheet, flow rate for both directions are almost identical.

    I am gonna eliminate a whole row (1/3) of the outdoor coil today & see what happen. I expect this would re-balance the supply & demand in heatpump mode, reduce the pressure loss, and also further increase airflow which also support higher saturation temp, etc,.
    The adverse effect is higher condensing temp in Cooling mode.

    What do you reckon, everyone?

    P/s:
    Thanks for all of your comments & interests so far. I find this forum of exceptional quality.
    Have a good new week, everyone.
    Last edited by Uni; 13-05-2012 at 11:12 PM.

  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    Gary & mikeref, I used the two (one) ways TXV as described in Emerson's article.
    I'm not sure what you mean. Are you saying both of your TXV's have the built-in check valves? Or are you saying that you are only using one TXV?

    Quote Originally Posted by Uni View Post
    I am gonna eliminate a whole row (1/3) of the outdoor coil today & see what happen.
    That would be a big mistake. Coil size is NOT the problem.
    Last edited by Gary; 14-05-2012 at 12:18 AM.

  19. #19
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    I am using one two-ways-TXV, or Two (one) way TXV as the manufacturer called it, same concept as in the article, Gary. One TXV with internal checkvalve used for both heating & cooling modes.

    What do you reckon about the proper solution?

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    You should have a two way TXV at each coil.

  21. #21
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Did you mean two traditional TXV & check valve? One for Heating, one for cooling?

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Each of the coils needs a TXV and a check valve ***OR*** each of the coils needs a TXV with a built-in check valve.

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

  24. #24
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Starved Evaporator Troubleshooting?

    Do you have a Bi-flow expansion valve.

    It is a single valve that allows expansion in either direction.

    I simple question when you said it was working in cooling was it cold out side?

  25. #25
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Gary, I have one indoor coil + one outdoor coil + one "whatever we call it" - two ways expansion valve in between + a reversing valve.

    Yes, mad fridge. It's a single valve that allows expansion in either direction . A single valve for both heating & cooling modes. If we look at Gary's picture, the only thermo bulb will be installed downstream between the Reversing valve & the suction tube. No check valve used because this TXV is two ways expansion. Gas flow rate for both direction is quite identical for any specific balancing pressure.

    As per my first post, It was at about 7C outdoor temperature and the unit was in heating mode.

    P/s: the term I used before, two-(one)-way-TXV, is from the manufacturer manual. This could have made confusion.
    Last edited by Uni; 14-05-2012 at 06:46 AM.

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?


  27. #27
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Starved Evaporator Troubleshooting?

    You said it was 7C when on heating but said "cooling was great" it would be great if the ambient was at 7C.
    Add some more refrigerant.

  28. #28
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Yep, Gary.

    Mad fridgie, 35C outdoor for cooling mate. You're not gonna cool down if it's 7C, aren't you?!

  29. #29
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    Yep, Gary.

    Mad fridgie, 35C outdoor for cooling mate. You're not gonna cool down if it's 7C, aren't you?!
    Struggling here how can it be 7C and 35C at the same time. Yes it will cool down if it is 7C outdoor ambient, very well indeed to well actually..

  30. #30
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    To clarify,

    Roughly it's a reverse cycle A/C system, so when we test the cool mode, we'll need 27C indoor/35C outdoor. In heating mode, we'll need 20C indoor/7C outdoor. No matter how you control the climate condition, it's international standard, or AS/NZS if we're Down Under. And, we can not do all tests at the same time, for sure.

    This' also an A/C system with heat mode as stated above, it's not for a cold room.

  31. #31
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Also as stated above, I'm very happy with the cooling mode. And if you put more gas in, it will affect the cooling mode. Don't forget we have to tune the cooling cycle for AU climate, like 48-50C outdoor.
    Last edited by Uni; 15-05-2012 at 12:51 AM.

  32. #32
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    To clarify,

    Roughly it's a reverse cycle A/C system, so when we test the cool mode, we'll need 27C indoor/35C outdoor. In heating mode, we'll need 20C indoor/7C outdoor. No matter how you control the climate condition, it's international standard, or AS/NZS if we're Down Under. And, we can not do all tests at the same time, for sure.

    This' also an A/C system with heat mode as stated above, it's not for a cold room.
    Best explain who you are and what you are doing. I was under the impression you were just a service guy having a few problems.
    The standards you talking about refer to performance, you can run/test any system under any number of conditions to find out if it working or not.

  33. #33
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    I believe the questions & solutions is what matters here. That will be helpful for all & is the purpose of this forum, I think. Our impression about others is not.

    Please get back to what matters.

  34. #34
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    What is the subcooling at the TXV inlet?

  35. #35
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Starved Evaporator Troubleshooting?

    So is this machine out in the field at someones house or shop or factory. Did it work and now it does not.
    or are you trying to test/develop a new system.
    It is important to how the questions are answered.

  36. #36
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Almost no subcool, Gary. That's one reason why I was hesitated to increase charge.

    This is a home made machine & never worked before I built & tested it. That's why I mentioned
    Things can be changed including outdoor airflow (which is currently quite high already, 670m3/h on high), outdoor coil size and tube configuration (can make it bigger or smaller or whatever tube arrangement), charge amount can also be change slightly (may have adverse effect because of relatively small indoor coil), can't fit a bigger TXV which is already oversize.

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    In heating mode, charge it until the subcooling is 10-15F.

  38. #38
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Starved Evaporator Troubleshooting?

    I have very low Evaporating temp (-28C), very low Suction pressure, very high SH (30K, although 2-TXV is set to minimum SH, wide open)
    Almost no subcool, Gary. That's one reason why I was hesitated to increase charge.
    To increase condenser SC, you need to add gas. To increase evap Tsat & reduce SH, you need to add gas.Your charge-determination trials need to be performed for BOTH modes, then compared.

    If, in one mode, there is a huge difference, you may need to find a place (buffer) to store the excess charge. Perhaps a receiver? There may be pro's & con's against this mind.

    In my view, the equation that needs to be in your head:
    Evap heat [kW] + compressor input [kW] = condenser heat [kW]

    If you move out of balance too far, in either mode, the system will be rather difficult to fine-tune.
    Last edited by desA; 16-05-2012 at 07:37 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  39. #39
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Currently in heating mode,
    Evap heat [kW] + compressor input [kW] >>> condenser heat [kW] (physically very small)

    Yep, I'll do the charge determination test again. Currently for both modes, in high load conditions, I've got approx 57C condensing temp, can afford a bit more.

    Thanks, everyone.

  40. #40
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Starved Evaporator Troubleshooting?

    Uni Try to post pictures showing the collectors of the big condenser and the evaporator too.

    One thing you have wrong is Evapheat+Compressor input IS ALWAYS APPROXIMATE EQUAL TO Condenser heat. Never greater than.

    Contrary to what many people think, large condensers do not condense because they need a certain velocity for the correct heat transfer to occur, thus the null subcooling at the outlet.

    In a normal condenser this is solved by reducing the number of circuits like you try to do but this condenser must also work as an evaporator so the collector design becomes a mayor issue.

    Bi-flow valves are used only on compact systems where the separation of refrigerant phases does not occur before the distributor or you will have a malfunctioning distributor which will cause maldistribution in the evaporator so it will never work!
    Last edited by aramis; 17-05-2012 at 05:24 PM. Reason: Ach! please don't ask!
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  41. #41
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Gents,

    Just added up to 35% more gas yesterday in 50g steps and it yield not so impressive different. If you experienced the charge determination test, major parameters will eventually (another 20-30% more gas?) shoot up after a flat region I was observing. However, I just could not justify that much charge amount for such a little changes in a small domestic system.

    aramis,

    I meant outdoor coil (evap. now) + comp >>> indoor coil capacity (cond. now). please kindly correct me if I'm still wrong. Also, I agree with you about potential issues so I do not have any type of collectors or fancy distributors, just direct inlet & outlet tubing. This clarifies the concerns with bi-flow valve Vs distributor as well.

    I'll try a smaller outdoor coil in heating mode today & see the effects.

    Thanks again for all current and forthcoming suggestions.

    Cheers,

  42. #42
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    Gents,

    Just added up to 35% more gas yesterday in 50g steps and it yield not so impressive different. If you experienced the charge determination test, major parameters will eventually (another 20-30% more gas?) shoot up after a flat region I was observing. However, I just could not justify that much charge amount for such a little changes in a small domestic system.
    What was the subcooling? Pressures?

    Quote Originally Posted by Uni View Post
    Also, I agree with you about potential issues so I do not have any type of collectors or fancy distributors, just direct inlet & outlet tubing.
    Is the liquid line feeding into the bottom on both coils?
    Last edited by Gary; 17-05-2012 at 11:47 PM.

  43. #43
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    Gents,

    I meant outdoor coil (evap. now) + comp >>> indoor coil capacity (cond. now). please kindly correct me if I'm still wrong. Also, I agree with you about potential issues so I do not have any type of collectors or fancy distributors, just direct inlet & outlet tubing. This clarifies the concerns with bi-flow valve Vs distributor as well.
    Sorry to sound nerdy but you refer to the condenser’s nominal capacity. The actual capacity should be about equal, like desA said. Only about because the compressor is giving off energy as vibration, noise and some heat to ambient directly and also depends on insulation.

    If the pressure drop of the evaporator in heating mode is high this will fool the bi-flow valve thinking it has a high superheat and tend to close. It works like an internaly equalized TXV in heating.

    You should try to measure what Gary is asking in the heating cycle and I would add both pressures (high, low) plus temperature of refrigerant at the inlet of the evaporator (between the valve and the evaporator insulating the probe) this way we can estimate the evaporator’s pressure drop. This measurements must be as simultaneous as you possibly can.

    Also check that there is not noticeable pressure drop (or temperature drop) in the reversing valve in the suction tubes (in and out) just to make sure it is opening the suction correctly.

    If you are not measuring your pressures at the compressor valves, please indicate where exactly.
    Last edited by aramis; 18-05-2012 at 03:36 AM. Reason: changed ex to in
    Well, did anybody ever dream of calling Aramis a coward? No, certainly not!

  44. #44
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Gary View Post
    What was the subcooling? Pressures?
    SC 1K (almost no changes), at +35% charge Pd was up 0.07MPa, Ps was up 0.05MPa.

    Quote Originally Posted by Gary View Post
    Is the liquid line feeding into the bottom on both coils?
    The liquid line feeds into the bottom on both coils.

  45. #45
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Keep charging.

    If the TXV were restricted, there would be a liquid back up and high subcooling.

    Low subcooling + high superheat = low charge

  46. #46
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    Got your point, Gary. But it's a lot of cost doubling up the charge.

    Can we explain it this way?

    If

    - TXV is max open (should be, I dipped it into a bow of hot water to check) ,
    - and the indoor coil (cond) is small (not enough to make any sufficient SC),
    - and the outdoor coil (evap) is too big, even though the valve is max open, still not feeding enough.

    So the results are:

    - Indoor coil does reject lots of heat (Td >= 25C), but No SC or minimum SC, there may be not fully liquid leaving the coil (?),
    - Valve not restricted, feeding as much as it could,
    - Starving outdoor coil created low suction pressure, high SH, then inturn, could not support very higher head pressure.

  47. #47
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    (Td >= 25C)...
    Are you saying the saturated condensing temperature is 25K higher than the coil air on temp?

  48. #48
    Join Date
    Sep 2008
    Location
    Australia
    Posts
    59
    Rep Power
    16

    Re: Starved Evaporator Troubleshooting?

    It was Air off temp - air on temp over the indoor coil in heating (ambient 24C outdoor/30C indoor)


    p/s: Have good weekend, everyone.

  49. #49
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Quote Originally Posted by Uni View Post
    It was Air off temp - air on temp over the indoor coil in heating (ambient 24C outdoor/30C indoor)
    That would be the dT, not the Td... and it is way too high, indicating insufficient air flow.

  50. #50
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Starved Evaporator Troubleshooting?

    Okay... let's re-think this:

    The oversized outdoor coil is an advantage in cool mode. It is also an advantage in heat mode at very low outdoor temperature. The downside would be high compressor inlet superheat in heat mode in warm weather... possibly resulting in high discharge temperature.

    I'm thinking we should put it in cool mode, adjust the TXV and the refrigerant charge... and generally fine tune it.

    Then we can deal with the heat mode, paying particular attention to the discharge temperature.